Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Bradley Bassett via RE-wrenches
I have no experience with the Hawaii connection, but another choice for a tap connector is the Ilso GTA type with cover. You don't have to cut the tapped line and don't rely on piercing it. Brad Bassett Application Engineer (ret.) 1985 Solar Eng Svcs -> Applied Power -> Applied Power (Idaho Power

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread david quattro via RE-wrenches
Type 1: You’ll be limited to 100A solar because the Utility conductors you’re attaching to are 100A. The Utility tap needs to immediately go to a fused disconnect switch, generally within 6ft (sometimes 10ft) and within line of sight of the meter. Fuses need AIC rating equivalent to that of the S

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Jerry Shafer via RE-wrenches
Does the utility allow line side tie in and then you should not need to be concerned about the 100 amp main as long as you have the wire size correct. Many utilities are not allowing line side tap however. Fun times On Tue, Aug 8, 2023, 8:11 AM Dana Orzel via RE-wrenches < re-wrenches@lists.re-wr

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Darryl Thayer via RE-wrenches
I need clarification; however, here is my interpretation for you. The utility feeds the meter and then the 100A breaker. Then you want this 100A breaker to feed the 220A bus panel. This 220A panel then supplies through a 100A breaker the house load. The solar also feeds the 220A panel. If the sola

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Dana Orzel via RE-wrenches
Correct  & The 225 amp bus bar gives us the busbar ampacity to accept the 120 amp back feed (includes the 25% factor) 22800w /240v = 95 amp On 8/8/2023 12:19 PM, Darryl Thayer via RE-wrenches wrote: I need clarification; however, here is my interpretation for you. The utility feeds the meter

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Jason Szumlanski via RE-wrenches
The Feeder Tap is our preferred method when available. However, I think you will find engineers who disagree that the tap can occur anywhere along the feeder. In my experience, PEs want to see that tap done with the downstream OCPD close to the tap. We would normally tap immediately before the subp