Correct  & The 225 amp bus bar gives us the busbar ampacity to accept the 120 amp back feed (includes the 25% factor)

22800w /240v = 95 amp


On 8/8/2023 12:19 PM, Darryl Thayer via RE-wrenches wrote:
I need clarification; however, here is my interpretation for you.
The utility feeds the meter and then the 100A breaker.
Then you want this 100A breaker to feed the 220A bus panel.
This 220A panel then supplies through a 100A breaker the house load.
The solar also feeds the 220A panel. If the solar exceeds 100A, and the house load is small, the meter breaker will disconnect, losing power to the solar and the load.

On Tue, Aug 8, 2023 at 10:11 AM Dana Orzel via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    Oh Wise folks!

    Attached is a wire schematic please review. & feel free to
    possibly use for yourself in the future.

    I am in a bind with an interconnection where I have an apartment 6
    pack meter  box with all 120-240v/100 amp breakers & assumed 100
    amp busbars. The apts. were a mid 1970's original build.  There
    are 4 apartment with 1 circuit/meter each & 1 house circuit/ meter
    for owners use.The breaker boxes are Sylvania (yuck). Originally I
    assumed a larger busbar due to 6 - 100 amp breakers & this was not
    the case. We all know about assuming...

    I consulted with W-2 who had assisted my lead installer in in the
    past from UT. He sent the following & though it makes sense to me,
    the utility is asking how I can have a 225 amp panel behind a 100
    amp breaker. My response was that all we are doing is  achieving a
    properly sized bus bar to accommodate the back feed.

    My Utility Idaho Power requires  interconnection with a meter that
    has a load on it. Solar only meters are not allowed. This is for
    the owners loads only & he has 1 meter per apt complex at 100amps
    each.

    I am wondering if any of you have used this connection adaption to
    achieve a larger array connection & how it went?

-- Dana Orzel Great Solar Works, Inc. C - 208.721.7003
    d...@solarwork.com Idaho Contractor - # 028765 Idaho PV # 028374
    "Responsible Technologies for Responsible People since 1988"
    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
Dana Orzel Great Solar Works, Inc. C - 208.721.7003 d...@solarwork.com Idaho Contractor - # 028765 Idaho PV # 028374 "Responsible Technologies for Responsible People since 1988"
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to