Hello. I'm wondering if there is a code reference for the allowable
clearance above a plumbing vent. I've run into several jurisdictions that
ask for the clearance to be at least 2x the diameter of the vent pipe. I'm
wondering if there are any code references to back this up or any code that
spe
The 2021 IPC (Section 903) requires vents to terminate at the height
specified by the AHJ (in fact the text of the document literally says "not
less than [NUMBER] inches (mm) above the roof" which I believe in general
is based on 6 inches above anticipated snow cover.
The 2021 IPC also specifical
Note that CA adopts UPC not IPC and the last time I checked there was no
exception to allow shorter vents under solar panels in the UPC, so it
differed from IPC allowance.
If this has changed, would be glad to be know about it!
Cheers,
Rebekah
On Fri, May 13, 2022, 10:51 AM Brian Mehalic via RE-w
What are you using for the RSD, I have found they all fault out except for
fire raptor, dont go with any features, keep it simple
Jerry
Jerry
On Tue, May 10, 2022, 10:17 AM Eric Smiley via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> A general question for those who have installed So
4 matches