Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Bryan Norkunas
Trying this again since my first link didn’t work, here is the link to the MFG specs for NON PV , low DC applications: https://ec.staubli.com/AcroFiles/Technical%20Info/PV_SOL-LVDC_(en).pdf For safety reasons Stäubli prohibits the use of thermoplastic PVC insulation cables.

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Blake Gleason
Bryan, Thank you for the link. I am confused by the "PVC" section you referenced. Here's the complete text: For safety reasons Stäubli prohibits the use of PVC cables. Cables made > from PVC can be connected to MC4-Evo 2 since the insulation material of the > connector (Polyamide) is suitable

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Bryan Norkunas
The MC4-Evo 2 isn’t the typical MC4 connector we are used to in the United States, these are commonly found in Europe, designed to meet European standards. Standard MC4 on the left, EVO-2 on the right pictured below: MC4 and MC4-Evo 2 portfolio first with new IEC certification The MC4

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Corey Shalanski
Blake, In addition to Bryan's notes, here is some unconfusing information directly from Stäubli's engineering dept: The answer is categorically no: *you cannot use THHN wires with MC4 > connectors.* There are several reasons for this: > 1. *Certification*: our MC4 connectors are certified to

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Blake Gleason
Corey, Thank you! Agreed, the message from Staubli's Eng dept is much less confusing (with the exception of the statement about THHN tending to be solid vs stranded). All - What are you folks using to transition from PV Wire to THHN/THWN-2 inside a junction box? We used to use split bolts, whic

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread Jerry Shafer
Wrenches Where did the thought come from about THHN and MC4, insulation is much thicker, releaf is the MC4 matches for USE/PV #10 wire is larger so you would have a poor or no seal. Also THHN is not weather/sunlight resistant. I had an inspector in Hawaii insist on MC4's connecting PV wire to THHN

Re: [RE-wrenches] MC4s are listed for THWN, right?

2021-04-26 Thread frenergy