Re: [RE-wrenches] Does a Neutral Count as a CCC

2016-04-24 Thread James Rudolph
Straight from Mike Holt: *Neutral Conductor* The neutral conductor of a 3-wire single-phase 120/240V system, or 4-wire 3-phase 120/208V or 277/408V wye-connected system isn’t considered a current-carrying conductor. The neutral conductor of a 3-wire circuit from a 4-wire 3-phase 120/208V or 277V

Re: [RE-wrenches] Does a Neutral Count as a CCC

2016-04-24 Thread Ray Walters
However, in this case, Peter's installing lots of 120 vac branch circuits, so all of those neutrals will be carrying full current (unless they are shared neutral circuits). Mike Holt's exception would apply to 240vac circuits if they had a neutral. Further, Holt's exception would not be appli