Hi there,
In a previous thread on this topic Chris Mason reported no problems at all
back-feeding PV derived AC into his gennie.
I quote Chris. "Best of all is they work together happily. My Kohler 12RES
and my SMA SB3000 seem to work together perfectly, without any issues.
Although wa
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of SunHarvest
Sent: Wednesday, January 16, 2013 9:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] off grid PV connected to generator
Finally got through to Outback. They said the GVFX could be wired with a genny
line-side of the inverter in ord
does the generator charge the batteries
if the genny is load-side of the inverter?
Eric
SunHarvest
- Original Message -
From: SunHarvest
To: RE-wrenches
Sent: Wednesday, January 16, 2013 8:47 AM
Subject: Re: [RE-wrenches] off grid PV connected to generat
At 12:53 PM 1/16/2013, you wrote:
Finally got through to Outback. They said the GVFX could be wired
with a genny line-side of the inverter in order for the genny to
charge the batteries and that this configuration could potentially
cause problems for the genny. The likelihood of the PV sending
ing the genset supply-side of the inverter, the
> question remains, for me at least, how does the generator charge the
> batteries if the genny is load-side of the inverter?
>
> Eric
> SunHarvest
>
> - Original Message -
> From: SunHarvest
> To: RE-wrenches
&
enny is load-side of the inverter?
Eric
SunHarvest
- Original Message -
From: SunHarvest
To: RE-wrenches
Sent: Wednesday, January 16, 2013 8:47 AM
Subject: Re: [RE-wrenches] off grid PV connected to generator
For claification, the two installs with which I'm concerned are:
o connect to an Outback tech (Katee Wood)...
Eric
SunHarvest
- Original Message -
From: David Katz
To: RE-wrenches
Sent: Wednesday, January 16, 2013 8:12 AM
Subject: Re: [RE-wrenches] off grid PV connected to generator
Phil,
If Eric is using the FX ot GTFX in an AC coupled mode
Phil,
If Eric is using the FX ot GTFX in an AC coupled mode, he would need to
disconnect the grid tie inverter when the generator was running. From the
thread, I cannot tell if this is his situation.
David Katz
Sent from my HTC smartphone on the Now Network from Sprint!
- Reply message --
Eric,
Good questions, and you hit on a number of topics so let me see if I can
address them one at a time, not necessarily in chronological order.
Yes, the optimal application for the GTFX / GVFX inverter series is grid
tie with battery backup. If you just want backup to the grid, the
traditiona
one of my biggest gripes about the outback fx series is only one ac input...
this was a major step backwards from its trace sw series predecessor.
if someone is going to want battery back up on a grid tied system, they surely
are going to want the ability to back that up with a generator. the ra
Hi Dan
Would like to know what they suggested besides changing it to a VFX?
Jay
Peltz power
Sent from my iPad
On Jan 15, 2013, at 1:54 PM, Dan Fink wrote:
> Talk to Outback. It's an easy fix, on-site.
> --
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckv
I did. They were less than helpful. At least the two or three different techs I
talked to. They sounded as green as me.
- Original Message -
From: Dan Fink
To: RE-wrenches
Sent: Tuesday, January 15, 2013 1:54 PM
Subject: Re: [RE-wrenches] off grid PV connected to generator
Talk to Outback. It's an easy fix, on-site.
--
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342 (voicemail)
On Tue, Jan 15, 2013 at 2:50 PM, SunHarvest wrote:
(snip)
> Further, I
s] off grid PV connected to generator
Best of all is they work together happily. My Kohler 12RES and my SMA SB3000
seem to work together perfectly, without any issues.
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrench
2012 8:18 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] off grid PV connected to generator
August –
I’ve seen this scenario and it is not pretty like William suggests.
From what I’ve seen, the problem is not so much the power of the PV
being more than the generator, but moreso if the 1)
Best of all is they work together happily. My Kohler 12RES and my SMA
SB3000 seem to work together perfectly, without any issues.
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.
horst
*Sent:* Wednesday, December 12, 2012 8:18 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] off grid PV connected to generator
August –
I’ve seen this scenario and it is not pretty like William suggests.
>From what I’ve seen, the problem is not so much the power of the PV b
August -
I've seen this scenario and it is not pretty like William suggests.
>From what I've seen, the problem is not so much the power of the PV being
more than the generator, but moreso if the 1) generator is synchronous or
non-synchronous with the inverted AC (sine wave) and 2) if the
Hi there,
Does it not depend on the size of the generator?
I know that solar grid tie into a diesel generator derived grid is done on
several pacific Islands.
Carl Emerson
At 02:07 PM 12/12/2012, you wrote:
Hi Wrenches,
I have a quick theoretical question related to trying to
I have watched this scenario happen with a the Sunny Island system AC
coupled to Sunny Island. There is a parameter called maximum reverse
generator power that you can program. It defaults at 100W I believe. If
the current feeding into the generator is greater than this parameter, the
Sunny Isla
August:
The apocalypse. No, seriously, this is a scenario not supported by any
manufacturer I know of. The report we have is it is likely the generator
will be damaged. I recommend against it.
William Miller
At 02:07 PM 12/12/2012, you wrote:
Hi Wrenches,
I have a quick theoretical que