Phil,
If Eric is using the FX ot GTFX in an AC coupled mode, he would need to 
disconnect the grid tie inverter when the generator was running.  From the 
thread, I cannot tell if this is his situation.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


----- Reply message -----
From: "Phil Undercuffler" <solarp...@gmail.com>
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] off grid PV connected to generator
Date: Tue, Jan 15, 2013 8:07 pm



Eric,

Good questions, and you hit on a number of topics so let me see if I can 
address them one at a time, not necessarily in chronological order.

Yes, the optimal application for the GTFX / GVFX inverter series is grid tie 
with battery backup.  If you just want backup to the grid, the traditional FX 
is a great solution.  If you need extended run-time and want to integrate a 
generator, then the Radian series is a better solution because it can not only 
integrate both grid and generator, but it can change its operating parameters 
based on which input it's connected to.

The SW, XW and Radian inverters are all capable of operating on-grid 
(grid-interactive or backup) or off-grid (with or without a generator).  
However, none will automatically disconnect the PV when the genny auto-starts, 
nor would I suggest that they should.  Realistically, the system should only 
start the genny when the batteries are near depletion -- if it's started, the 
batteries need all the help they can get.  Rather, the generator should only be 
disconnected (turned off) when the batteries reach the absorb setpoint.  BTW, I 
can't speak for everyone but none of those inverters have that functionality, 
at least not yet.

With 600 Watts of connected PV, I wouldn't worry about disconnecting the PV.  
Even with a small battery bank, the sun will set before that size of array 
drives the bank anywhere close to an absorb voltage.  Add another zero to the 
PV size and my answer would be different, of course.

Also, if you do wind up installing an automatic transfer switch with a 
battery-based inverter system, don't allow the ATS to control the generator 
starting, even if that flies against every tradition of the generator sales 
guy.  You don't want the genny running through every minute of the power 
outage, you want the system to start the genny only when the batteries are low.

Good luck with it, and enjoy the sun!

Phil



On Tue, Jan 15, 2013 at 1:50 PM, SunHarvest 
<e...@harvesthesun.com<mailto:e...@harvesthesun.com>> wrote:
Further, I recently installed a GVFX for a customer. I'm hearing from certain 
sources that the grid-tied line of inverters from Outback are not designed to 
interface with a generator. Really??

I was told by Outback to install a transfer switch line/supply side of the 
inverter; that this was the only way to interface the genny with the inverter; 
that the AC Hot In could come from grid or a genset. And indeed, this is the 
only way I can figure out how to get the genny to charge the batteries when the 
grid goes down. But then again, I don't have the extensive electrical 
background that allows me to think outside the box as often as I would 
like...that's why I'm posing my query here for the pros. In this Outback 
install I have to again advise the homeowner to open the PV breaker to the 
inverter during generator operation, right? Even though he has a modest 600W 
(STC) array and an 8.5kW Kohler genset. Hardly the opportunity for solar to 
feed back to the genny under the most sunny and cool of days. I'm more 
concerned with the Enphase install.

The Xantrex SW series inverters are fully capable of operating on-grid or 
off-grid with a genset. So do those inverters automatically disconnect the PV 
when the genny auto-starts? And with the Outback, is the Mate supposed to do 
the same (as long as the genny is operated by the auto-start and not a transfer 
switch)?


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to