Note that the language states min. service disconnect size, and not
specifically the size of the service. In the old days we would go round and
round w/the AHJ over this in OTG systems. In most cases we could point to the
"Service Disconnect" that was rated at least 100A this being the Main DC
o 60A.
Matt Lafferty
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Friday, August 27, 2010 5:10 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] minimum service
230.79(C):
230.79 Rating of Se
230.79(C):
230.79 Rating of Service Disconnecting Means.
The service disconnecting means shall have a rating not less than the
calculated load to be carried, determined in accordance with Part III,
IV, or V of Article 220, as applicable. In no case shall the rating be
lower than specified in 2