Re: [RE-wrenches] minimum service

2010-08-27 Thread Jeff Oldham
Note that the language states min. service disconnect size, and not specifically the size of the service. In the old days we would go round and round w/the AHJ over this in OTG systems. In most cases we could point to the "Service Disconnect" that was rated at least 100A this being the Main DC

Re: [RE-wrenches] minimum service

2010-08-27 Thread Matt Lafferty
o 60A. Matt Lafferty -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click Sent: Friday, August 27, 2010 5:10 AM To: RE-wrenches Subject: Re: [RE-wrenches] minimum service 230.79(C): 230.79 Rating of Se

Re: [RE-wrenches] minimum service

2010-08-27 Thread Dave Click
230.79(C): 230.79 Rating of Service Disconnecting Means. The service disconnecting means shall have a rating not less than the calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable. In no case shall the rating be lower than specified in 2