Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Darryl Thayer
Regarding 3 Power Walls PWs, more solar modules, and inverters. I hope this is helpful, I am always going to first principles. You did not mention what the customer expectations are. I see three common possibilities, 1) For backup power, in which case you need generation control, such as the AC

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Chris Sparadeo
Keep in mind that 7.5kW is max charge/discharge for 10 sec...it is NOT the continuous rate. This comes into play in the following scenario: Let’s say a single Powerwall 2 is at 50% SOC and there is a utility outage on a sunny day. The inverter is outputting 7kW AC and loads in the house are below

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Barton Churchill
You can just land the new PV to the same "generation" panel that already hosts the 3 Powerwalls and existing PV inverter output breakers. There should be no loads on this panel. The Powerwall AC coupled solar limit is 7.5 KW AC per Powerwall, note AC not DC. The DC rating is irrelevant here. If

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Jerry Shafer
Wrenches This customer with an orphan PW, not to compromise the factory warranty on the batteries, it would be safest to just grid tie any additional PV and not touch the existing system from the gateway down. Jerry NABCEP PV Inspector On Fri, Apr 16, 2021, 8:38 AM Kirk Herander, VSE wrote: > He

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Darryl Thayer
Hello, I hope this helps. I have very little PW experience, the one i was involved in had a 1741 transfer switch with grid monitoring on the mains. When the grid failed the switch would disconnect from the Grid and connect the PW to the panel or sub-panel. The PW charges from the AC source when i

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Glenn Burt
The manuals I have say 7.6kW(AC) per PW2 Glenn From: RE-wrenches On Behalf Of Jason Szumlanski Sent: Friday, April 16, 2021 9:46 PM To: RE-wrenches Subject: Re: [RE-wrenches] Powerwall 2 AC PV regulation I think the limit is now stated as 7.6kw if memory serves me right. Jason

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Jason Szumlanski
I think the limit is now stated as 7.6kw if memory serves me right. Jason On Fri, Apr 16, 2021, 12:11 PM Matt Partymiller wrote: > They used to advocate 7.9kW AC/DC per Powerwall. That number may have > gone down recently. Coupling an inverter on the line side of the backup > gateway will res

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-16 Thread Vincent Jolissaint
Hi Kirk, the maximum actual charge rate is 5kW per Powerwall. When you exceed that, or start getting full batteries, the Gateway tells the Powerwalls to frequency shift to 62-66 Hz. This takes the UL 1741 listed inverters out of the sweet spot, and they stop or curtail production. However, predict

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-16 Thread Matt Partymiller
They used to advocate 7.9kW AC/DC per Powerwall. That number may have gone down recently. Coupling an inverter on the line side of the backup gateway will resolve your issue of meeting homeowner demand. Tesla will want you to add a CT to that inverter to ensure it does not mess up their monit