You can just land the new PV to the same "generation" panel that already hosts the 3 Powerwalls and existing PV inverter output breakers. There should be no loads on this panel. The Powerwall AC coupled solar limit is 7.5 KW AC per Powerwall, note AC not DC. The DC rating is irrelevant here. If the combined PV AC inverter output is less than 22.5 kW the system will work fine. Tesla does have a list of approved PV inverters but unless you're looking to connect something over 3 years old it should be fine.
[cid:f7580fd8-6285-4e79-9ad8-512cb4416200]Barton Churchill Director, Power Division 2042 Stadium Drive Suite 2 • Bozeman, MT 59715 • (O) 406-587-2917 • (D) 406-589-4493 235 E. Broadway • Jackson, WY 83001 • (O) 307-200-2210 bchurch...@energy-1.net<mailto:blans...@energy-1.net> | www.energy-1.net<http://www.energy-1.net/> ________________________________ From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of Kirk Herander, VSE <kirkh@vermont.solar> Sent: Friday, April 16, 2021 9:13 AM To: re-wrenches@lists.re-wrenches.org <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Powerwall 2 AC PV regulation Hello all, I am adding more PV to an orphaned Powerwall 2 AC system (which is all new to me), -3- PW's stacked to total about 40kwh of usable storage. it presently has about 13kw of PV, though -2- SMA inverters, feeding into it through a common subpanel between the PW gateway and the main panel. I'm wondering if there is a limit to the amount of PV the powerwall can regulate/backoff (or use for battery charging) during a utility outage. What is the max PW charge rate? I need to add about 10 kw of PV to produce the owners goal of 100% coverage of electrical demand. If necessary for safety, i assume the extra pv inverter can be routed to the main panel, and then won't participate in battery charging if the grid goes down. Am I correct? Thanks. The PW manuals are of little use here. Kirk Herander / kirkh@vermont.solar<mailto:kirkh@vermont.solar> Owner|Principal, VT Solar, LLC Celebrating our 30th Anniversary 1991-2021!! www.vermont.solar<https://us-west-2.protection.sophos.com?d=outlook.com&u=aHR0cHM6Ly9uYW0wMi5zYWZlbGlua3MucHJvdGVjdGlvbi5vdXRsb29rLmNvbS8_dXJsPXd3dy52ZXJtb250c29sYXJub3cuY29tJmRhdGE9MDIlN0MwMSU3QyU3QzlmMDMzMGQ3NWEyNDQ4NzAxMTI0MDhkNjg1MzExODQxJTdDODRkZjllN2ZlOWY2NDBhZmI0MzVhYWFhYWFhYWFhYWElN0MxJTdDMCU3QzYzNjg0Mjg0MzIzMzQ3NzY0NSZzZGF0YT0wTmp5dUtlUWJFSzYyNDVTTm5rOFg0WG5QOVElMkIlMkJxdHZjQUxrZERnaHZrNCUzRCZyZXNlcnZlZD0w&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=T0V4VmVuWVp1a3A2UUVZOTRNRitLRWViVk1TM1o4Wll0MDNtSTg5WndOTT0=&h=257d32539c424fbdb09425b1e02ea242> dba Vermont Solar Engineering 802.863.1202
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org