You can just land the new PV to the same "generation" panel that already hosts 
the 3 Powerwalls and existing PV inverter output breakers. There should be no 
loads on this panel. The Powerwall AC coupled solar limit is 7.5 KW AC per 
Powerwall, note AC not DC. The DC rating is irrelevant here. If the combined PV 
AC inverter output is less than 22.5 kW the system will work fine. Tesla does 
have a list of approved PV inverters but unless you're looking to connect 
something over 3 years old it should be fine.


[cid:f7580fd8-6285-4e79-9ad8-512cb4416200]Barton Churchill
Director, Power Division
2042 Stadium Drive Suite 2 • Bozeman, MT 59715 • (O) 406-587-2917 • (D) 
406-589-4493
235 E. Broadway • Jackson, WY 83001 • (O) 307-200-2210
bchurch...@energy-1.net<mailto:blans...@energy-1.net>   |    
www.energy-1.net<http://www.energy-1.net/>


________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of Kirk 
Herander, VSE <kirkh@vermont.solar>
Sent: Friday, April 16, 2021 9:13 AM
To: re-wrenches@lists.re-wrenches.org <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Powerwall 2 AC PV regulation

Hello all,
I am adding more PV to an orphaned Powerwall 2 AC system (which is all new to 
me), -3- PW's stacked to total about 40kwh of usable storage. it presently has 
about 13kw of PV, though -2- SMA inverters, feeding into it through a common 
subpanel between the PW gateway and the main panel. I'm wondering if there is a 
limit to the amount of PV the powerwall can regulate/backoff (or use for 
battery charging) during a utility outage. What is the max PW charge rate? I 
need to add about 10 kw of PV to produce the owners goal of 100% coverage of 
electrical demand.
If necessary for safety, i assume the extra pv inverter can be routed to the 
main panel, and then won't participate in battery charging if the grid goes 
down. Am I correct? Thanks. The PW manuals are of little use here.


Kirk Herander / kirkh@vermont.solar<mailto:kirkh@vermont.solar>

Owner|Principal, VT Solar, LLC

Celebrating our 30th Anniversary 1991-2021!!

www.vermont.solar<https://us-west-2.protection.sophos.com?d=outlook.com&u=aHR0cHM6Ly9uYW0wMi5zYWZlbGlua3MucHJvdGVjdGlvbi5vdXRsb29rLmNvbS8_dXJsPXd3dy52ZXJtb250c29sYXJub3cuY29tJmRhdGE9MDIlN0MwMSU3QyU3QzlmMDMzMGQ3NWEyNDQ4NzAxMTI0MDhkNjg1MzExODQxJTdDODRkZjllN2ZlOWY2NDBhZmI0MzVhYWFhYWFhYWFhYWElN0MxJTdDMCU3QzYzNjg0Mjg0MzIzMzQ3NzY0NSZzZGF0YT0wTmp5dUtlUWJFSzYyNDVTTm5rOFg0WG5QOVElMkIlMkJxdHZjQUxrZERnaHZrNCUzRCZyZXNlcnZlZD0w&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=T0V4VmVuWVp1a3A2UUVZOTRNRitLRWViVk1TM1o4Wll0MDNtSTg5WndOTT0=&h=257d32539c424fbdb09425b1e02ea242>

dba Vermont Solar Engineering

802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to