I’m curious what the PW 3 surge rating is?
Anyone know?
And where would it be found, I can’t find it.
jay
> On Dec 21, 2024, at 4:03 PM, Dave Angelini Offgrid Solar via RE-wrenches
> wrote:
>
>
>
> No warranty is no warranty. Would love it if Elon would go offgrid.
>
> The model 3 is almo
No warranty is no warranty. Would love it if Elon would go offgrid.
The model 3 is almost there. I did build an xw into a powerwall with bad
electronics. It is still running.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso.
David, Wrenches,
I would not recommend that as it may be a warranty issue down the road and
last l heard is it must be monitored at all times and if there is not a
grid even though it's AC coupled could ba there issue.
Fun times
On Sat, Dec 21, 2024, 9:05 AM David Coale via RE-wrenches <
re-wrenc
Thanks, Vincent. This is the information I needed.
I did read that at least 1 MCI is needed even if you do not require RSD. The MCI
instructions are a bit confusing. I know for RSD you need one at the start of a
string and at least one every three modules, but it's unclear if you need the
MCI-1 o
Last time I spoke with Tesla, they did not support either fully off-grid or
installations not connect to the internet. Have they changed their policy
on this?
On Tue, Sep 10, 2024 at 8:19 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Correct, but there are some
Correct, but there are some off-grid scenarios where a generator with a
transfer switch would be an adequate redundancy for rare solar/battery
capacity deficiencies.
On Tue, Sep 10, 2024, 8:02 PM Dave Angelini Offgrid Solar via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I hear 3 st
I hear 3 still can't use a generator from youtube. Pretty cool other
than that.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2024-09-10 4:37 pm, Jason Szumlanski via RE-wrenches wrote:
Ce
Regarding 3 Power Walls PWs, more solar modules, and inverters. I hope
this is helpful, I am always going to first principles. You did not
mention what the customer expectations are. I see three common
possibilities, 1) For backup power, in which case you need generation
control, such as the AC
Keep in mind that 7.5kW is max charge/discharge for 10 sec...it is NOT the
continuous rate. This comes into play in the following scenario:
Let’s say a single Powerwall 2 is at 50% SOC and there is a utility outage
on a sunny day. The inverter is outputting 7kW AC and loads in the house
are below
You can just land the new PV to the same "generation" panel that already hosts
the 3 Powerwalls and existing PV inverter output breakers. There should be no
loads on this panel. The Powerwall AC coupled solar limit is 7.5 KW AC per
Powerwall, note AC not DC. The DC rating is irrelevant here. If
Wrenches
This customer with an orphan PW, not to compromise the factory warranty on
the batteries, it would be safest to just grid tie any additional PV and
not touch the existing system from the gateway down.
Jerry
NABCEP PV Inspector
On Fri, Apr 16, 2021, 8:38 AM Kirk Herander, VSE
wrote:
> He
Hello, I hope this helps. I have very little PW experience, the one i was
involved in had a 1741 transfer switch with grid monitoring on the mains.
When the grid failed the switch would disconnect from the Grid and connect
the PW to the panel or sub-panel. The PW charges from the AC source when
i
The manuals I have say 7.6kW(AC) per PW2
Glenn
From: RE-wrenches On Behalf Of
Jason Szumlanski
Sent: Friday, April 16, 2021 9:46 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Powerwall 2 AC PV regulation
I think the limit is now stated as 7.6kw if memory serves me right.
Jason
I think the limit is now stated as 7.6kw if memory serves me right.
Jason
On Fri, Apr 16, 2021, 12:11 PM Matt Partymiller wrote:
> They used to advocate 7.9kW AC/DC per Powerwall. That number may have
> gone down recently. Coupling an inverter on the line side of the backup
> gateway will res
Hi Kirk, the maximum actual charge rate is 5kW per Powerwall. When you
exceed that, or start getting full batteries, the Gateway tells the
Powerwalls to frequency shift to 62-66 Hz.
This takes the UL 1741 listed inverters out of the sweet spot, and they
stop or curtail production. However, predict
They used to advocate 7.9kW AC/DC per Powerwall. That number may have gone
down recently. Coupling an inverter on the line side of the backup gateway
will resolve your issue of meeting homeowner demand. Tesla will want you to
add a CT to that inverter to ensure it does not mess up their monit
The Powerwall 2 is only AC coupleable to a PV system.-GlennSent from my
'smart'phone, so please excuse typos and spelling errors.-- Original
message--From: Dave Angelini Offgrid SolarDate: Sun, Jan 10, 2021 12:57
PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] PowerwallHello Wrenches !
The l
Hi Dave,
Yes, your understanding is correct. No access to DC terminals. Definitely
not a great off-grid solution and is complicated and clunky at best to
integrate a gen.
Best,
Chris
On Sun, Jan 10, 2021 at 12:57 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
> Hello Wrenches !
The things people spend money on and the reasons are so varied that dollar
analysis is just part of the decision.
It can be almost priceless to stay in your home after the utility goes off
during a wildfire. Keeping the smoke out, the cool air inside, and not
having to go to a shelter or motel are
Hi Hilton,
We've done the math for our installed cost on the Powerwall 2. Certainly,
it wouldn't make sense to purchase it just for energy savings alone with
current California residential electricity tariffs. However, most folks are
buying it primarily for backup purposes and then a little bit of
20 matches