Re: [RE-wrenches] PowerWall 3 in an off-grid system?

2024-12-21 Thread jay via RE-wrenches
I’m curious what the PW 3 surge rating is? Anyone know? And where would it be found, I can’t find it. jay > On Dec 21, 2024, at 4:03 PM, Dave Angelini Offgrid Solar via RE-wrenches > wrote: > > > > No warranty is no warranty. Would love it if Elon would go offgrid. > > The model 3 is almo

Re: [RE-wrenches] PowerWall 3 in an off-grid system?

2024-12-21 Thread Dave Angelini Offgrid Solar via RE-wrenches
No warranty is no warranty. Would love it if Elon would go offgrid. The model 3 is almost there. I did build an xw into a powerwall with bad electronics. It is still running. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso.

Re: [RE-wrenches] PowerWall 3 in an off-grid system?

2024-12-21 Thread Jerry Shafer via RE-wrenches
David, Wrenches, I would not recommend that as it may be a warranty issue down the road and last l heard is it must be monitored at all times and if there is not a grid even though it's AC coupled could ba there issue. Fun times On Sat, Dec 21, 2024, 9:05 AM David Coale via RE-wrenches < re-wrenc

Re: [RE-wrenches] Powerwall 3 (contd)

2024-09-11 Thread Jason Szumlanski via RE-wrenches
Thanks, Vincent. This is the information I needed. I did read that at least 1 MCI is needed even if you do not require RSD. The MCI instructions are a bit confusing. I know for RSD you need one at the start of a string and at least one every three modules, but it's unclear if you need the MCI-1 o

Re: [RE-wrenches] Powerwall 3

2024-09-10 Thread Chris Sparadeo via RE-wrenches
Last time I spoke with Tesla, they did not support either fully off-grid or installations not connect to the internet. Have they changed their policy on this? On Tue, Sep 10, 2024 at 8:19 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Correct, but there are some

Re: [RE-wrenches] Powerwall 3

2024-09-10 Thread Jason Szumlanski via RE-wrenches
Correct, but there are some off-grid scenarios where a generator with a transfer switch would be an adequate redundancy for rare solar/battery capacity deficiencies. On Tue, Sep 10, 2024, 8:02 PM Dave Angelini Offgrid Solar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I hear 3 st

Re: [RE-wrenches] Powerwall 3

2024-09-10 Thread Dave Angelini Offgrid Solar via RE-wrenches
I hear 3 still can't use a generator from youtube. Pretty cool other than that. Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-09-10 4:37 pm, Jason Szumlanski via RE-wrenches wrote: Ce

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Darryl Thayer
Regarding 3 Power Walls PWs, more solar modules, and inverters. I hope this is helpful, I am always going to first principles. You did not mention what the customer expectations are. I see three common possibilities, 1) For backup power, in which case you need generation control, such as the AC

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Chris Sparadeo
Keep in mind that 7.5kW is max charge/discharge for 10 sec...it is NOT the continuous rate. This comes into play in the following scenario: Let’s say a single Powerwall 2 is at 50% SOC and there is a utility outage on a sunny day. The inverter is outputting 7kW AC and loads in the house are below

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Barton Churchill
You can just land the new PV to the same "generation" panel that already hosts the 3 Powerwalls and existing PV inverter output breakers. There should be no loads on this panel. The Powerwall AC coupled solar limit is 7.5 KW AC per Powerwall, note AC not DC. The DC rating is irrelevant here. If

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-18 Thread Jerry Shafer
Wrenches This customer with an orphan PW, not to compromise the factory warranty on the batteries, it would be safest to just grid tie any additional PV and not touch the existing system from the gateway down. Jerry NABCEP PV Inspector On Fri, Apr 16, 2021, 8:38 AM Kirk Herander, VSE wrote: > He

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Darryl Thayer
Hello, I hope this helps. I have very little PW experience, the one i was involved in had a 1741 transfer switch with grid monitoring on the mains. When the grid failed the switch would disconnect from the Grid and connect the PW to the panel or sub-panel. The PW charges from the AC source when i

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Glenn Burt
The manuals I have say 7.6kW(AC) per PW2 Glenn From: RE-wrenches On Behalf Of Jason Szumlanski Sent: Friday, April 16, 2021 9:46 PM To: RE-wrenches Subject: Re: [RE-wrenches] Powerwall 2 AC PV regulation I think the limit is now stated as 7.6kw if memory serves me right. Jason

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-17 Thread Jason Szumlanski
I think the limit is now stated as 7.6kw if memory serves me right. Jason On Fri, Apr 16, 2021, 12:11 PM Matt Partymiller wrote: > They used to advocate 7.9kW AC/DC per Powerwall. That number may have > gone down recently. Coupling an inverter on the line side of the backup > gateway will res

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-16 Thread Vincent Jolissaint
Hi Kirk, the maximum actual charge rate is 5kW per Powerwall. When you exceed that, or start getting full batteries, the Gateway tells the Powerwalls to frequency shift to 62-66 Hz. This takes the UL 1741 listed inverters out of the sweet spot, and they stop or curtail production. However, predict

Re: [RE-wrenches] Powerwall 2 AC PV regulation

2021-04-16 Thread Matt Partymiller
They used to advocate 7.9kW AC/DC per Powerwall. That number may have gone down recently. Coupling an inverter on the line side of the backup gateway will resolve your issue of meeting homeowner demand. Tesla will want you to add a CT to that inverter to ensure it does not mess up their monit

Re: [RE-wrenches] Powerwall

2021-01-10 Thread Glenn Burt
The Powerwall 2 is only AC coupleable to a PV system.-GlennSent from my 'smart'phone, so please excuse typos and spelling errors.-- Original message--From: Dave Angelini Offgrid SolarDate: Sun, Jan 10, 2021 12:57 PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] PowerwallHello Wrenches ! The l

Re: [RE-wrenches] Powerwall

2021-01-10 Thread Chris Sparadeo
Hi Dave, Yes, your understanding is correct. No access to DC terminals. Definitely not a great off-grid solution and is complicated and clunky at best to integrate a gen. Best, Chris On Sun, Jan 10, 2021 at 12:57 PM Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > Hello Wrenches !

Re: [RE-wrenches] Powerwall and other Li

2018-02-15 Thread Dave Angelini Offgrid Solar
The things people spend money on and the reasons are so varied that dollar analysis is just part of the decision. It can be almost priceless to stay in your home after the utility goes off during a wildfire. Keeping the smoke out, the cool air inside, and not having to go to a shelter or motel are

Re: [RE-wrenches] Powerwall and other Li

2018-02-15 Thread August Goers
Hi Hilton, We've done the math for our installed cost on the Powerwall 2. Certainly, it wouldn't make sense to purchase it just for energy savings alone with current California residential electricity tariffs. However, most folks are buying it primarily for backup purposes and then a little bit of