Hi Nick,
I see (2011) 705.12 (d) where it talks about " supplying branch circuits as
the area where it changes.
ie w/o branch circuits then all circuits are protected by the breakers as long
as the main buss isn't exceeded by the solar input of course.
But in putting in that metering device p
Nick,
Forgive me as I am referencing NEC 2008. But 690.64 (B) Load Side, "...and
where this distribution equipment is capable of supplying multiple branch
circuits, or feeders, or both...shall comply..."
To the extent the accumulation panel is NOT capable of supplying other
circuits, then NONE
Hi Rich
If there are no AC loads, only the inverters then there is no derate for the
panel buss.
However if you connect any other loads such as a metering device, now you have
to apply the 120% rule.
Jay
Peltz Power
On Jan 22, 2012, at 4:53 AM, "Rich Nicol" wrote:
> Good Morning Wrenche