Hi Rich

If there are no AC loads, only the inverters then there is no derate for the 
panel buss.
However if you connect any other loads such as a metering device, now you have 
to apply the 120% rule.

Jay

Peltz Power





On Jan 22, 2012, at 4:53 AM, "Rich Nicol" <r...@solartechvt.com> wrote:

> Good Morning Wrenches,
> I’m wondering if anyone has an advice on preferred methods and 
> component/panel recommendations for paralleling multiple inverters. The 
> proposed system will utilize 4 SMA6000 inverters (100 amps) and will be a 
> ground mounted system with inverters located outdoors in the cold frigid 
> temperatures of Vermont in a farmer’s field so the panel where we complete 
> the parallel connections needs to be outdoor rated (although it will be 
> sheltered from the worst of the elements). It will be a standalone system 
> with a dedicated utility power drop/meter for the system. My understanding of 
> using a load center in this applications is that the 120% rule will apply as 
> it does in a typical installation per NEC690.64(B)(2)with the bus amp rating 
> for the load center based upon the inverter feed side as well as the over 
> current device on the utility side.
> Any input regarding preferred panels and configuration is appreciated.
> Thanks
> Rich
>  
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to