Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Ray Walters
Based on many successful installs, I'd say a 3/4 HP pump is not a problem at all, and that the Magnum could easily run a 1-1/2 HP submersible pump. 2 HP probably, but that's where you start worrying. The Franklin Subpak controller can be used on regular AC pumps and not only offers constant pre

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Larry Crutcher, Starlight Solar Power Systems
Yes Drake, I stand corrected, I was picturing the micro inverters feeding the input rather than coupling the output of the Magnum. To your original question, I think you would have to be consuming more power than the PV array alone can provide before the Magnum voltage would drop with the pump l

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Drake
We use a protective relay, unless using Sunny Islands. In this case, the relay will be controlled by the programmable AUX relay's12 V signal. Magnum does have a phase shifting function, but does not recommend relying on it. At 04:40 PM 7/3/2014, you wrote: Wrenches I have not seen either a

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Jerry Shafer
Wrenches I have not seen either a OB, Trace or Magnum do a even far job of charge control or voltage limiting for the batteries during AC coupling as this is when the transformer is basicly going backwards, it can and does but even outback says you need to do a AC discounting means or AC or DC load

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Drake
Hi Larry, In this case, the Enphase will AC couple with the Magnum in the protected loads panel. The AC out of the Magnum provides the micro grid to which the Enphase connects. If charging exceeds loads, when the grid is down, power will go to the batteries (up to the high battery voltage se

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Drake, If the Enphase are online, up to 60 amps (30A @ 240V) can be transferred through the Magnum inverter to loads. The inverter is not providing power to loads at that time. If the Enphase go offline, the Magnum takes over using power from the battery. If the load is greater than your Enp

Re: [RE-wrenches] Magnum and Pumps

2014-07-03 Thread Drake
This information helps greatly. I really appreciate all of your expert advice. One other wild card in the installation is that the inverter is going to be AC coupled with an Enphase system. The Enphase system will contribute greatly to the overall power available in the protected loads panel.

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread dave
RE Ellison" : What has been everybody’s experience with Full River Batteries?   Bob   From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]  On Behalf Of  Roy Butler Sent: Wednesday, July 02, 2014 3:12 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Magnum an

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread RE Ellison
What has been everybody’s experience with Full River Batteries? Bob From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Roy Butler Sent: Wednesday, July 02, 2014 3:12 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Magnum and Pumps

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Jason Szumlanski
Sorry, typo - that's a 48V string (one string of 8 batteries). Jason Szumlansk​i Fafco Solar On Wed, Jul 2, 2014 at 3:15 PM, Jason Szumlanski wrote: > ​Even at 9600W, which is above the 5 second surge rating of the inverter,​ > we're looking at about 200A on the DC side, which would be a 1-h

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Jason Szumlanski
​Even at 9600W, which is above the 5 second surge rating of the inverter,​ we're looking at about 200A on the DC side, which would be a 1-hr rate on an L-16 string. While that is high, it should not be an issue. Even at the 1ms surge of 16,800W, a 48 string of L16's should be able to handle that.

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Roy Butler
Sweetthanks for that info, I stand corrected! Roy Butler NABCEP Certified Solar PV Installer® NYSERDA eligible PV & wind installer IREC Certified Master Trainer™ for Small Wind Installer Four Winds Renewable Energy, LLC 8902 Route 46, Arkport, NY 14807 607-324-9747 www.f

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Roy, The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he should be fine. Larry On Jul 2, 2014, at 12:35 PM, Roy Butler wrote: I haven't seen anyone mention the battery bank. If I understand correctly, there's a single string of sealed L16 batteries on this inverter.

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Roy Butler
I haven't seen anyone mention the battery bank. If I understand correctly, there's a single string of sealed L16 batteries on this inverter. I have my doubts as to whether or not that bank can provide the high current the inverter needs to start this load.

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Jason Szumlanski
To further qualify my statements, the inverter will start the pump without issue, but I should echo the warnings by others that if there are other loads present, especially other motor loads that could start ​concurrently, you may experience issues. As long as your customer understands the limitati

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Kevin Pegg
Hi Drake, To answer question "does this seem like a good combination" I would reply no. Keep in mind well pumps often kick in concurrently with other large loads, washing machines, dishwashers, etc. I'm sure the MS 4448 PAE will start the pump ok, but forewarn customer of brownouts when

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Jason Szumlanski
For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, but that startup current is likely less than you well pump. I'm goi

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Larry Crutcher, Starlight Solar Power Systems
If you have a clamp on meter that can capture inrush current (I use a Fluke 337 for this) you can get a good idea of the starting current needed. One problem is that while backing up the house, you will likely have other loads operating when the pump starts which will decrease the available surg

Re: [RE-wrenches] Magnum and Pumps

2014-07-02 Thread Allan Sindelar
Drake, As a normal CYA, I'll always gently let a customer know that this (or any) particular combination of inverter and load sometimes proves incompatible, just in case the unexpected happens. (We once had a MS4448 that would not reliably start and run a condensi