Hi Drake,

If the Enphase are online, up to 60 amps (30A @ 240V) can be transferred 
through the Magnum inverter to loads. The inverter is not providing power to 
loads at that time. If the Enphase go offline, the Magnum takes over using 
power from the battery. If the load is greater than your Enphase system can 
provide, the Magnum will transfer to battery power based on the VAC dropout 
setting. You probably want to use the UPS mode (read ME-ARC manual about this).

The new Magnum MSH models can combine AC input power and battery power to 
increase the total AC output capacity for starting heavy loads. 

Larry



On Jul 3, 2014, at 7:59 AM, Drake <drake.chamber...@redwoodalliance.org> wrote:

This information helps greatly. I really appreciate all of your expert advice.

One other wild card in the installation is that the inverter is going to be AC 
coupled with an Enphase system. The Enphase system will contribute greatly to 
the overall power available in the protected loads panel. But, with Magnum's 
slow voltage response I'm not sure if the Enphase system will drop off line 
when the pump surges, or if the Enphase power will be available to help with 
the startup surge. 

Any insights on this?

Thank you,

Drake
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to