Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread William Miller
August: I read the referenced report. It does not address the concern I raised— that is the breaker specified unbonds a system that I believe is supposed to be bonded. William > On Jul 23, 2019, at 8:38 AM, August Goers wrote: > > Hi William - > > This article is a few years old, but I thi

Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread August Goers
Hi William - Check out the Solarpro Magazine archive May/June 2017 issue page 34: it addresses "functional grounded PV systems." https://docs.wixstatic.com/ugd/d49ff9_ccc99efe7b344f6a945ca2e00f8a71d8.pdf And the definition found in 2017 NEC 690.2: [image: image.png] Yes, the normally grounded w

Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread Harry Mahon
pient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you. From: RE-wrenches On Behalf Of Darryl Thayer Sent: Monday, July 22, 2019 10:18 PM To: William Miller ; RE-wrenches Subject: Re: [RE-wrenches] DC

Re: [RE-wrenches] DC Bonding battery systems

2019-07-23 Thread August Goers
Hi William - This article is a few years old, but I think describes ground fault detection issues well: http://www.solarabcs.org/about/publications/reports/blindspot/pdfs/inverter_groundfault-2013.pdf I don't have experience (at least since the late 90s) with the type of GFD breaker you describe

Re: [RE-wrenches] DC Bonding battery systems

2019-07-22 Thread Darryl Thayer
Hi Bill, I have thought about it also. The ground fault detection interruption system does elevate one of the conductors to voltage. This makes it hazardous. However, it also protects from a PV hot to ground arc fault. There are three types of arc faults in PV systems, the ground fault arc, the

Re: [RE-wrenches] DC Bonding battery systems

2019-07-22 Thread Dave Angelini Offgrid Solar
I can see your point but I know from direct experience that the GFCI in an XW system will trip during a close lightning strike. I have seen this along with a few clients. The XW system has a series of escalating faults that will shut down the inverter if the strike is close. To me it is worth it