Wrenches – I am no code expert, but wanted to chime in to this important 
discussion.

Rapid shutdown (690.12) does not deal (directly) with arc faults at all.  The 
initiation of rapid shutdown is generally a manual process that a first 
responder triggers to reduce shock hazard. The RS system is not required to 
monitor the system for any faults on the DC side.

690.11 (DC arc faults) requires a system to “detect and interrupt arcing faults 
resulting from a failure in the intended continuity of a conductor, connection, 
module or other system component”(2017)  (by definition a series arc) – and 
note that this has nothing necessarily to do with a ground fault. A PV module 
connector that is being pulled apart and the current is arcing across the gap 
between pins is exactly what this is for – a very good chance that arcs create 
high enough temperature – even at low current – to start a fire.

A ground fault does not need to generate an arc (though likely will).  A ground 
fault is the unintentional electrical connection of a conductor to the 
grounding system.  Removal of insulation of a conductor that is resting on a 
grounded piece of metallic racking will do.  The conductor does not need to be 
physically compromised, just exposed.

Back to the original thread point - I agree that the sudden change in voltage 
state of the conductors is not optimal, but the delta between DC pos and DC neg 
will not change.  And the intent is that the GFDI fuse will blow when part of 
that conductive path has been referenced to ground (by the fault) out in the 
array anyway.  So nominal voltage would not be measured out in the array when 
the ground fault system is needed, right before and after the fuse blows.

The Bakersfield fire was the result of many faults occurring due to improper 
installation techniques, but led to the acknowledgement that the fuse grounding 
method presents a “blind spot” – the inability to detect a ground fault on the 
grounded conductor itself.  That fault will not necessarily present a hazard 
(no change in voltage and thus current of the already grounded conductor) but 
it also will NOT trigger the ground fault detection system.  Another fault 
occurring in the array then may have a return fault path for current that the 
GFDI fuse blowing cannot stop.  Much better summary than I can give here:
http://www.solarabcs.org/about/publications/reports/blindspot/

Best regards –
Mike


SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]<http://www.facebook.com/pages/SMA-America/140290312717395>[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg]<http://twitter.com/SMA_America>
 [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg] 
<http://www.smainverted.com/>  [Linkedin Logo] 
<http://www.linkedin.com/company/364675>  
[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg] 
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] 
<http://smaadvance.com/signup/>
[cid:image008.jpg@01D45E26.3FF7F550]


This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Darryl Thayer
Sent: Monday, July 22, 2019 10:18 PM
To: William Miller <will...@millersolar.com>; RE-wrenches 
<re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] DC Bonding battery systems

Hi Bill, I have thought about it also.  The ground fault detection interruption 
system does elevate one of the conductors to voltage.  This makes it hazardous. 
 However, it also protects from a PV hot to ground arc fault.  There are three 
types of arc faults in PV systems, the ground fault arc, the series arc fault, 
and the parallel arc fault.  It is the parallel arc that was addressed in the 
2017 NEC via module-level shutdown.  The intent of 690.11 can not be addressed 
without 2017 690.12.b(2) where the detection of an arc must shutdown the array 
currents.

On Mon, Jul 22, 2019 at 3:42 PM William Miller 
<will...@millersolar.com<mailto:will...@millersolar.com>> wrote:
Wrenches:

Here is a question that has bothered me for some time:  If one is using a GFD 
(ground fault detection) breaker on a PV feeder(s) to a battery inverter 
system, the state of the industry is to use a breaker with an extra 0.5 or 1 
amp pole.  This section of the breaker connects, or bonds the DC negative, or 
grounded conductor, to the grounding system.

In order for the GFD breaker to work one needs to isolate the grounded bus bar 
(negative).  If there is a ground fault the breaker opens and breaks the bond.

This goes very much against my conceptualization of how a bonding system should 
work.  The bond should never be broken, particularly when there is a fault in 
the system.  When this breaker opens, either manually or by an overcurrent 
condition on any pole, the DC bond is removed for all portions of the DC system.

There is a prominent personality in the industry that often presents academic 
opinions on solar related electrical issues in articles and in seminars.  This 
person claimed to have invented this GFD system, but when pressed to comment on 
the concerns mentioned above, changed the subject.

I believe ground fault protection is important.  I just don’t believe the 
method the industry has offered is really effective in solving the issues 
presented in a ground fault scenario.

I believe similar issues present on non-battery PV systems with the simple fuse 
in the ground system found on many inverters.  I know some troubleshooting 
guides warn of energized parts in ground fault conditions.

Have any of you thought about these concerns?  Are my concerns valid?  What are 
your policies on this subject?

Thanks in advance for any insight.

William Miller

Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.millersolar.com%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C8530e26b4e5d4bca4eee08d70f24c44e%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636994522897601786&sdata=R09%2B%2FvdKnZC36oAW6Vm4QKTEN%2B%2FFPmo5%2Fq8A6YB1Uus%3D&reserved=0>
CA Lic. 773985

Quote of the month:  “As they age, batteries transition from energy
storage devices to energy consuming devices.“ W. Miller

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C8530e26b4e5d4bca4eee08d70f24c44e%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636994522897601786&sdata=Pk8n5F0OqrHz4XQ5HqNWIv03A6Xqp0U%2F06aGH7ddHfY%3D&reserved=0>

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C8530e26b4e5d4bca4eee08d70f24c44e%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636994522897611784&sdata=lIy2A4xtpdmYCeJ4CM%2FsbXlFv5hNC040NAWJjM3ylmQ%3D&reserved=0>

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C8530e26b4e5d4bca4eee08d70f24c44e%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636994522897611784&sdata=jqo%2BLlLSI0md9JRczKGrHKTk6ipM0eFtfBDEeAL9k%2FQ%3D&reserved=0>

Check out or update participant bios:
www.members.re-wrenches.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.members.re-wrenches.org&data=02%7C01%7Cmichael.mahon%40sma-america.com%7C8530e26b4e5d4bca4eee08d70f24c44e%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636994522897621776&sdata=r07yak5Fa1r019pzEQZcO9Vy2F%2BrnyI0TdQoPIfyUew%3D&reserved=0>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to