Re: [RE-wrenches] Bonding Rails

2009-11-18 Thread Kirpal Khalsa
. > > > ---- Original Message ---- > Subject: Re: [RE-wrenches] Bonding Rails > From: Kirpal Khalsa > To: RE-wrenches > Date: 2009/11/17 19:29 > > Hey GuysUnirac recently changed their requirement to 2 clips between >> each module...one on the upper rail and

Re: [RE-wrenches] Bonding Rails

2009-11-18 Thread Dave Click
- Original Message Subject: Re: [RE-wrenches] Bonding Rails From: Kirpal Khalsa To: RE-wrenches Date: 2009/11/17 19:29 Hey GuysUnirac recently changed their requirement to 2 clips between each module...one on the upper rail and one on the lower rail..therefore by my count you

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Kirpal Khalsa
ts.re-wrenches.org] On Behalf Of Dave Click > Sent: Tuesday, November 17, 2009 1:09 PM > To: RE-wrenches > Subject: Re: [RE-wrenches] Bonding Rails > > Yes, that's correct. In my answer I was just rephrasing it to say you'd > need twice as many WEEBs as you think. As I

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Peter Parrish
Subject: Re: [RE-wrenches] Bonding Rails Yes, that's correct. In my answer I was just rephrasing it to say you'd need twice as many WEEBs as you think. As I understand it, the intent of this layout is to give the installer two chances to bond each module properly to the rail. Un

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Dave Click
rail), B&C (bottom rail), etc. DKC ---- Original Message ---- Subject: Re: [RE-wrenches] Bonding Rails From: Peter Parrish To: 'RE-wrenches' Date: 2009/11/17 15:55 On page 8 it would appear that we need TWO WEEB clips bonding modules A and B to rails #1 and #2 and another TWO WEE

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Peter Parrish
-wrenches.org] On Behalf Of Dave Click Sent: Tuesday, November 17, 2009 12:14 PM To: RE-wrenches Subject: Re: [RE-wrenches] Bonding Rails Peter, (1) it appears that per the WEEB installation manual: http://www.we-llc.com/Datasheets/104-0404-08-008.pdf (page 8) you need to have one WEEB per module

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Dave Click
Peter, (1) it appears that per the WEEB installation manual: http://www.we-llc.com/Datasheets/104-0404-08-008.pdf (page 8) you need to have one WEEB per module rather than one for every other module as you suggest. (2) 690.43 Equipment Grounding. Exposed non–current-carrying metal parts of

Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Michael Kelly
Peter, I've never used the ProSolar rails, so I can't speak to 1). On 2), yes, you must bond the rails with a listed device if they are not bonded to the modules. The nice thing about the WEEB is that it allows one to bond the modules and rails together, and then you can pick up the bond from th