Peter,

(1) it appears that per the WEEB installation manual:
http://www.we-llc.com/Datasheets/104-0404-000008-008.pdf
(page 8) you need to have one WEEB per module rather than one for every other module as you suggest.

(2) 690.43 Equipment Grounding.
Exposed non–current-carrying metal parts of module frames, equipment, and conductor enclosures shall be grounded in accordance with 250.134 or 250.136(A) regardless of voltage.

I guess the latter answer depends on whether your AHJ considers the rails "exposed"-- I would, so in this situation I'd have lugs on each module and each rail.

DKC

-------- Original Message --------
Subject: [RE-wrenches] Bonding Rails
From: Peter Parrish <peter.parr...@calsolareng.com>
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Date: 2009/11/17 14:56

We have been using WEEB clips on all of our installations for over a year now. We include the WEEB data/installation sheets in our permit package and patiently point out the clips to inspectors who haven’t seen the WEEB system yet.

Two questions:

(1) For ProSolar rails, can we use one WEEB clip to bond two adjacent modules (say, modules A and B) on the upper rail (say, rail #1) and then use a second WEEB clip to bond the next two adjacent modules (say, modules C and D) on the lower rail (say, rail #2) and then use a listed lay-in lug (with in our case a WEEB clip) to bond to either rail #1 or #2 to continue the grounding?

(2) If we DON”T use WEEB clips and use the conventional bonding methodology per module manufacturer’s instructions (proper location on the module, and listed screws, washers and nuts), do we have to ALSO bond the rails? We have an inspector in Pasadena, CA that is requiring this, but this is the first time we have been required to do so. Perhaps in the past year in ignorant bliss we have missed an important development? Or have we been dodging bullets for seven years and not even knowing it?

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com <mailto:peter.parr...@calsolareng.com> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

------------------------------------------------------------------------

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to