Phil,
NEC 690.17 says "Where all terminals of the disconnecting means may be
energized..." It would take a pretty rare malfunction of a grid
connected inverter to energize the load terminals of the utility
disconnect. But we have some AHJs that require this label on every ac
disconnect, all
Hi Phil,
Four out of the six of utilities that we deal with here in Arizona
require an external AC disconnect, and yes, we do install the plaque.
About half of the utilities explicitly require it, the other half don't.
I agree that is a confusing label, possibly leading service personnel to
Wrenches,
Our utilities require an external AC disconnect between the inverter and the
point of interconnection, located next to the meter. In the past, we have
marked this switch with the language in 690.17 (although no AHJ or utility
has required it). Because we generally argue against the nec