My main jurisdiction (Los Angeles City) has a utility with its own
service manual with their own requirements. Through experience we
know what they require, and it often has nothing to do with NEC.
If you bring up NEC to them, they usually laugh at you.
Nick Vida__
Marv:
The moral of this story: Never leave home without your Rule 21!
Wm
PS: Just kidding. The moral is actually: know the rules and don't let
yourself get pushed around.
wm
At 03:56 PM 10/2/2012, you wrote:
I had a similar situation with my own PV system many years ago. The
utility
s.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Tuesday, October 02, 2012 3:22 PM
To: Wrenches
Subject: [RE-wrenches] Utility disconnect
I just finished a job on a home where the utility didn't require the utility
disco. They contend that the service disconn
If this is simply a Code consideration, then the NEC does not require a
visible/lockable disconnect. You can refer to this SolarABCs document for a
thorough discussion of the subject:
http://www.solarabcs.org/about/publications/reports/ued/pdfs/ABCS-05_studyreport.pdf
On Oct 2, 2012, at 5:21 P
I just finished a job on a home where the utility didn't require the utility
disco. They contend that the service disconnect on the "farmer panel" meter
base will work for them. I said cool and didn't put one in. The inspector said
he couldn't sticker the project because the utility disco was