Thanks for the reply August. I’m working to get in touch with the engineer so
we’ll see what they say.
I agree balancing the tap on all parallel conductors sounds like it would avoid
the possibility of any issue, but I can’t think of what the problem would be if
current from the grid were decr
Hi Garrison,
This is a new one for me - normally we always balance everything when
dealing with paralleled conductors. NEC 310.10(H) talks about conductors in
parallel and I can't see anything the explicitly forbids what you
explained. To be safe, I think it is worth contacting the PE to double
ch
Hi Wrenches,
When making a supply side connection on parallel sets of conductors is it
required to tap all conductors on each phase?
I have a set of plans with an 800A interconnection on a 1200A service. Service
has three parallel sets of 500MCM. Plans call for tapping just two conductors
on