Robin had a comment on the breaker issue...
I'll just copy and paste since he says it better than I can for this
kind of stuff.
boB
Square D breakers are thermal breakers and are never used on PV
combiners. I am not familiar with any solar applications where thermal
breakers are used on a r
Dan
Hydraulic actuated breakers like the Classic Heiniman GJ,used in off grid
battery based systems ( now made by Carlon and Airpax, since Henimans's
patent ran out) it is very critical that they be used in the vertical
position as is marked on the breaker's chassis. I know this from
experience
To:
RE-wrenches
Date:
11/11/2013 10:09 AM
Subject:
Re: [RE-wrenches]
Square D Disconnects
If the box is NEMA 3R, it needs to be mounted vertically to shed
water. If it is a sealed NEMA 4X rated unit, it can be mounted at any angle.
At 02:49 PM 11/11/2013, you wrote:
Hi Wrenches,
There is no "implication" other than confirming how the disco
is tested, and thus certified. It probabl
ectric.com/solar | Address: 250 South Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Bob-O Schultze
To:
RE-wrenches
Date:
11/11/2013 10:09 AM
Subject:
Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.
S
Bob O..thank you, you got to the heart of my original questionI am
not questioning the OCPD ratingsjust the can mounted at a slope
equivalent to the roof slope.Typically if we have rooftop OCPD they are
high voltage fuse holders and fuses or the Outback and Midnite solar
breakers...
Dan,
I think this thread applied not to OCDs but to an unfused 600VDC disconnect can
mounted on a roof which is less than vertical.
Bob-O
On Nov 11, 2013, at 9:21 AM, Exeltech wrote:
Wrenches,
There appears to be some misinformation getting into this thread.
The "trip" mechanism within standard
Wrenches,
There appears to be some misinformation getting into this thread.
The "trip" mechanism within standard thermal over-current protective devices
("OCP devices") is mechanically spring-loaded, and is triggered by heat.
Eric mentions below that Square D breakers are tested in a vertical o
Address: 250 South Vasco Rd., Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From: Kirpal Khalsa <mailto:solarwo...@gmail.com>
To: RE-wrenches
<mailto:re-wrenches@lists.re-wrenches.org>
Date: 11/07/2013 01:42 PM
Subject: [RE-wrenches] Square D
ss:* 250 South Vasco Rd., Livermore, CA 94551
>
> [image: []] <http://www.schneider-electric.htm>
> *** Please consider the environment before printing this e-mail
>
>
>
> From: Kirpal Khalsa
> To: RE-wrenches
>
> Date: 11/07/2013 01:42 PM
> Subject: [RE-
Subject: [RE-wrenches]
Square
D Disconnects mounted on the slope of the roof.
Sent by:
re-wrenches-boun...@lists.re-wrenches.org
Hi Folks!!!
Anyone aware of minimum slope requirements for Squa
ermore, CA 94551
[]
*** Please consider the environment before printing this e-mail
From: Kirpal Khalsa
To: RE-wrenches
Date: 11/07/2013 01:42 PM
Subject: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Sent by: re-wrenches-boun...@lists.re-wrenches.org
Hi Folks!!!
Midnight now has a multi-string 600V rooftop disco.
Bob-O
On Nov 9, 2013, at 8:14 AM, Kirpal Khalsa wrote:
Thank you all for the ideas and infoin many parts of Oregon you are
required to have a rooftop fireman's disconnectwe have been using a variety
of methods...for small residential w
Thank you all for the ideas and infoin many parts of Oregon you are
required to have a rooftop fireman's disconnectwe have been using a
variety of methods...for small residential we are currently using the
midnite solar box with the disconnect handle and their 600vdc breaker but
this only w
Drummond
Sent: Friday, November 08, 2013 12:59 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D Disconnects mounted on the slope of the
roof.
15 degrees off of vertical is my understanding for standard RBs. So no,
can't do that. Cheers good friend.
On Nov 7, 2013 2:42 PM, "Kir
s.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Drummond
Sent: Thursday, November 07, 2013 10:59 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D Disconnects mounted on the slope of the
roof.
15 degrees off of vertical is my understanding for standard RBs. So no,
Vasco Rd.,
Livermore, CA 94551
*** Please consider the environment before printing this e-mail
From:
Kirpal Khalsa
To:
RE-wrenches
Date:
11/07/2013 01:42 PM
Subject:
[RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Sent by:
re-wrenches-boun...@lists.re-wrenches.org
15 degrees off of vertical is my understanding for standard RBs. So no,
can't do that. Cheers good friend.
On Nov 7, 2013 2:42 PM, "Kirpal Khalsa" wrote:
>
> Hi Folks!!!
> Anyone aware of minimum slope requirements for Square D 321RB
> disconnectsCan they be mounted on rails parallel to the s
Hi Folks!!!
Anyone aware of minimum slope requirements for Square D 321RB
disconnectsCan they be mounted on rails parallel to the slope of the
roof like Outback and Midnite solar combiner boxes(down to a 3/12 pitch)
I can't seem to find any notes stating the limitations in manufacturer
document