Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread b...@midnitesolar.com
Robin had a comment on the breaker issue... I'll just copy and paste since he says it better than I can for this kind of stuff. boB Square D breakers are thermal breakers and are never used on PV combiners. I am not familiar with any solar applications where thermal breakers are used on a r

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Bill Hoffer
Dan Hydraulic actuated breakers like the Classic Heiniman GJ,used in off grid battery based systems ( now made by Carlon and Airpax, since Henimans's patent ran out) it is very critical that they be used in the vertical position as is marked on the breaker's chassis. I know this from experience

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Gary Willett
To: RE-wrenches Date: 11/11/2013 10:09 AM Subject: Re: [RE-wrenches] Square D Disconnects

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Drake
If the box is NEMA 3R, it needs to be mounted vertically to shed water. If it is a sealed NEMA 4X rated unit, it can be mounted at any angle. At 02:49 PM 11/11/2013, you wrote: Hi Wrenches, There is no "implication" other than confirming how the disco is tested, and thus certified. It probabl

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Eric . Bentsen
ectric.com/solar | Address: 250 South Vasco Rd., Livermore, CA 94551 *** Please consider the environment before printing this e-mail From: Bob-O Schultze To: RE-wrenches Date: 11/11/2013 10:09 AM Subject: Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. S

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Kirpal Khalsa
Bob O..thank you, you got to the heart of my original questionI am not questioning the OCPD ratingsjust the can mounted at a slope equivalent to the roof slope.Typically if we have rooftop OCPD they are high voltage fuse holders and fuses or the Outback and Midnite solar breakers...

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Bob-O Schultze
Dan, I think this thread applied not to OCDs but to an unfused 600VDC disconnect can mounted on a roof which is less than vertical. Bob-O On Nov 11, 2013, at 9:21 AM, Exeltech wrote: Wrenches, There appears to be some misinformation getting into this thread. The "trip" mechanism within standard

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Exeltech
Wrenches, There appears to be some misinformation getting into this thread. The "trip" mechanism within standard thermal over-current protective devices ("OCP devices") is mechanically spring-loaded, and is triggered by heat. Eric mentions below that Square D breakers are tested in a vertical o

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Drake
Address: 250 South Vasco Rd., Livermore, CA 94551 *** Please consider the environment before printing this e-mail From: Kirpal Khalsa <mailto:solarwo...@gmail.com> To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org> Date: 11/07/2013 01:42 PM Subject: [RE-wrenches] Square D

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Kirpal Khalsa
ss:* 250 South Vasco Rd., Livermore, CA 94551 > > [image: []] <http://www.schneider-electric.htm> > *** Please consider the environment before printing this e-mail > > > > From: Kirpal Khalsa > To: RE-wrenches > > Date: 11/07/2013 01:42 PM > Subject: [RE-

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Ray Walters
Subject: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. Sent by: re-wrenches-boun...@lists.re-wrenches.org Hi Folks!!! Anyone aware of minimum slope requirements for Squa

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Drake
ermore, CA 94551 [] *** Please consider the environment before printing this e-mail From: Kirpal Khalsa To: RE-wrenches Date: 11/07/2013 01:42 PM Subject: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. Sent by: re-wrenches-boun...@lists.re-wrenches.org Hi Folks!!!

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Bob-O Schultze
Midnight now has a multi-string 600V rooftop disco. Bob-O On Nov 9, 2013, at 8:14 AM, Kirpal Khalsa wrote: Thank you all for the ideas and infoin many parts of Oregon you are required to have a rooftop fireman's disconnectwe have been using a variety of methods...for small residential w

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread Kirpal Khalsa
Thank you all for the ideas and infoin many parts of Oregon you are required to have a rooftop fireman's disconnectwe have been using a variety of methods...for small residential we are currently using the midnite solar box with the disconnect handle and their 600vdc breaker but this only w

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-09 Thread William Dorsett
Drummond Sent: Friday, November 08, 2013 12:59 AM To: RE-wrenches Subject: Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. 15 degrees off of vertical is my understanding for standard RBs. So no, can't do that. Cheers good friend. On Nov 7, 2013 2:42 PM, "Kir

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-08 Thread Bill Brooks
s.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Drummond Sent: Thursday, November 07, 2013 10:59 PM To: RE-wrenches Subject: Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. 15 degrees off of vertical is my understanding for standard RBs. So no,

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-08 Thread Eric . Bentsen
Vasco Rd., Livermore, CA 94551 *** Please consider the environment before printing this e-mail From: Kirpal Khalsa To: RE-wrenches Date: 11/07/2013 01:42 PM Subject: [RE-wrenches] Square D Disconnects mounted on the slope of the roof. Sent by: re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-07 Thread Mark Drummond
15 degrees off of vertical is my understanding for standard RBs. So no, can't do that. Cheers good friend. On Nov 7, 2013 2:42 PM, "Kirpal Khalsa" wrote: > > Hi Folks!!! > Anyone aware of minimum slope requirements for Square D 321RB > disconnectsCan they be mounted on rails parallel to the s

[RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-07 Thread Kirpal Khalsa
Hi Folks!!! Anyone aware of minimum slope requirements for Square D 321RB disconnectsCan they be mounted on rails parallel to the slope of the roof like Outback and Midnite solar combiner boxes(down to a 3/12 pitch) I can't seem to find any notes stating the limitations in manufacturer document