Hi Bill,
So Funny
I had assumed Carl had placed a disconnect in the attic so i stated the
obvious art 110 reference.
Ive taken this type of installation to the extreme in this past in a new
construction situation.
I surrounded emt in 3" of concrete from roof entry to basement.
My Opinion, get ready
Carl, Pat,
I guess I'm somewhere in between. We have /alway/s installed a
touchsafe/fused disco on the roof adjacent to the array, no matter how
many strings and dive into the attic (if there is one) from there. I
don't think I've ever put a disco in the attic, the roof seems more
a
y, January 04, 2016 12:05 PM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)
You could show them the 2011 or 2014 NEC, both of which clarify this
(rather than making a new rule), so the inspector might accept this
rational. The numbers are a
Hi Carl,
I've moved away from this type of installation since alot of the inspectors
in this area just don't like it.
I avoid getting into "code confrontations" with them and prefer to impress
them rather than depress them.
Have you looked at article 110 regarding working clearances?
Also I've cons
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Daniel Young
Sent: Monday, January 04, 2016 12:05 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)
You could show them the 2011 or 2014 NEC, both of which clarify this (rather
than ma
ProfessionalTM: Cert #031508-90
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Carl Adams
Sent: Monday, January 04, 2016 10:59 AM
To: RE-wrenches
Subject: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)
Fellow Wrenches,
We recently failed an
Hi Carl,
Given that you are using SE equipment. I'm guessing that locking out the DC
disco or AC side to shut the array down wasn't an option the inspector wanted?
I thought that is one of the reasons for using SE?
Jay
Peltz power.
> On Jan 4, 2016, at 7:58 AM, Carl Adams wrote:
>
> Fel
Fellow Wrenches,
We recently failed an inspection on a new PV installation
We are operating under the 2008 code
I have attached a small sketch of our conduit routing to clarify things.
Inspectors note post inspection ...provide a photovoltaic disconnecting
means per 690.14 (C)(1)
During his insp