2016-01-06 Thread Patrick Shortell
Hi Bill, So Funny I had assumed Carl had placed a disconnect in the attic so i stated the obvious art 110 reference. Ive taken this type of installation to the extreme in this past in a new construction situation. I surrounded emt in 3" of concrete from roof entry to basement. My Opinion, get ready

[RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-06 Thread frenergy
Carl, Pat, I guess I'm somewhere in between. We have /alway/s installed a touchsafe/fused disco on the roof adjacent to the array, no matter how many strings and dive into the attic (if there is one) from there. I don't think I've ever put a disco in the attic, the roof seems more a

Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-06 Thread Christopher Warfel
y, January 04, 2016 12:05 PM *To:* 'RE-wrenches' *Subject:* Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1) You could show them the 2011 or 2014 NEC, both of which clarify this (rather than making a new rule), so the inspector might accept this rational. The numbers are a

Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-05 Thread Patrick Shortell
Hi Carl, I've moved away from this type of installation since alot of the inspectors in this area just don't like it. I avoid getting into "code confrontations" with them and prefer to impress them rather than depress them. Have you looked at article 110 regarding working clearances? Also I've cons

Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-04 Thread Dana
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Daniel Young Sent: Monday, January 04, 2016 12:05 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1) You could show them the 2011 or 2014 NEC, both of which clarify this (rather than ma

Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-04 Thread Daniel Young
ProfessionalTM: Cert #031508-90 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams Sent: Monday, January 04, 2016 10:59 AM To: RE-wrenches Subject: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1) Fellow Wrenches, We recently failed an

Re: [RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-04 Thread Jay
Hi Carl, Given that you are using SE equipment. I'm guessing that locking out the DC disco or AC side to shut the array down wasn't an option the inspector wanted? I thought that is one of the reasons for using SE? Jay Peltz power. > On Jan 4, 2016, at 7:58 AM, Carl Adams wrote: > > Fel

[RE-wrenches] Source Circuit Disconnect - 690.14 (C)(1)

2016-01-04 Thread Carl Adams
Fellow Wrenches, We recently failed an inspection on a new PV installation We are operating under the 2008 code I have attached a small sketch of our conduit routing to clarify things. Inspectors note post inspection ...provide a photovoltaic disconnecting means per 690.14 (C)(1) During his insp