Carl, Pat,

I guess I'm somewhere in between. We have /alway/s installed a touchsafe/fused disco on the roof adjacent to the array, no matter how many strings and dive into the attic (if there is one) from there. I don't think I've ever put a disco in the attic, the roof seems more accessible, visible. Why always install a disco on the roof?...just the way I am and have been doing it long before the 2014NEC rapid shutdown (still working with 2011 here). I like the idea of being able to stop power from entering the house envelope. Most times this (getting into the attic) is most sensible here due to snow, as in sliding/creeping snow.

Somewhat related: I recently got a call from a new PV-on-the-roof installation, you know that dreaded one: " There's a leak coming from the can light over my sink which is just below the PVs you installed on my roof last month" I went out there that day, climbed into the attic and after looking at all the "evidence" came up with this: Most can lights have the insulation removed from that immediate area so the "can" is exposed to unconditioned attic temps which around here have been in the teens, any moisture from cooking in the kitchen would rise, enter the can and freeze...I came down from the attic armed with my explanation and alas, much pasta had been cooked and then strained in the sink the prior night. By the time I had arrived the dripping had stopped because their turning on the light that morning was enough to melt the frost in the can and produce a few minutes of dripping....enough dripping to call me (I must have been on their speed dial!).

Happy New Year all,

Bill

Feather River Solar Electric

On 1/5/2016 10:47 AM, Patrick Shortell wrote:
Hi Carl,
I've moved away from this type of installation since alot of the inspectors in this area just don't like it. I avoid getting into "code confrontations" with them and prefer to impress them rather than depress them.
Have you looked at article 110 regarding working clearances?
Also I've considered a cut in the insulation of a ungrounded source circuit conductor in grounded metal conduit inside a dwelling. Maybe i'm looking to deeply into it but I'd rather keep source circuit conductors on the exterior of a dwelling. It's hard to back track with the customer when he's been sold on the conduit being hidden and then having to eventually concede to the AHJ. Sometimes having your inspector review your installation plan before you install builds a good solid relationship with him and avoids costly reworking.
I'd rather be happy than right.
Just Saying
Pat

On Mon, Jan 4, 2016 at 10:58 AM, Carl Adams <[email protected] <mailto:[email protected]>> wrote:

    Fellow Wrenches,

    We recently failed an inspection on a new PV installation
    We are operating under the 2008 code
    I have attached a small sketch of our conduit routing to clarify
    things.

    Inspectors note post inspection ...provide a photovoltaic
    disconnecting means per 690.14 (C)(1)

    During his inspection the inspector was unhappy that we had
    entered the attic space with the DC source circuits, saying we
should have run the conduit across the roof and kept it outside. Since we entered the building we would need to add a DC disconnect
    in the attic to meet code.  My thought is that we fall under the
    exception listed (690.31(E)) since all source circuit internal to
    the dwelling are in metallic raceways.  I'd like to hear other
    wrenches chime in on this.

    Our reason for routing things as we did was to keep the
    installation aesthetics first class and minimize unsightly conduit
    runs.

    Code section follows

    690.14 Additional Provisions. Photovoltaic disconnecting
    means shall comply with 690.14(A) through (D).690.14

    (C) Requirements for Disconnecting Means. Means
    shall be provided to disconnect all conductors in a building
    or other structure from the photovoltaic system conductors.
    (1) Location. The photovoltaic disconnecting means shall
    be installed at a readily accessible location either on the
    outside of a building or structure or inside nearest the point
    of entrance of the system conductors.
    Exception: Installations that comply with 690.31(E) shall
    be permitted to have the disconnecting means located remote
    from the point of entry of the system conductors.
    The photovoltaic system disconnecting means shall not
    be installed in bathrooms.

     690.31 (E) reads as follows
    (E) Direct-Current Photovoltaic Source and Output
    Circuits Inside a Building. Where direct-current photovoltaic
    source or output circuits of a utility-interactive inverter
    from a building-integrated or other photovoltaic system are
    run inside a building or structure, they shall be contained in
    metal raceways, or metal enclosures, from the point of penetration
    of the surface of the building or structure to the
    first readily accessible disconnecting means. The disconnecting
    means shall comply with 690.14(A) through (D).


    With Regards
    Carl Adams, President
    SunRock Solar, LLC
    513.290.9072 <tel:513.290.9072> (cell)
    513.766.6025 <tel:513.766.6025> (office)


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





--
Patrick A. Shortell
/Licensed Master Electrician/
/Certified Solar Installer/
71 Oregon Street
Long Beach N.Y. 11561
cell: 516-477-0221






_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to