Hello Robin and boB.
Ryans Midnite video of the Birdhouse and rapid
shutdown disconnects is amazing. It does look
like you are producing a means of implementing this new code rule.
In many situations, the rapid shutdown
requirement certainly makes sense. In a large
system where high voltag
HI Dan,
If you are doing 24v battery or below, you should be able to ignore the battery
rapid shutdown part.
IE under 30v
jay
peltz power
On Aug 30, 2014, at 2:04 PM, Dan Fink wrote:
> Dave; I feel your pain as do many others.
> I feel like I've been Rick-rolled on the whole 690.12 thing. As
Dave; I feel your pain as do many others.
I feel like I've been Rick-rolled on the whole 690.12 thing. As a
firefighter, I thought rapid shutdown was a great idea for roof mounted
arrays. Shut down fast from a central location on the ground, get up on the
roof, do what needs to be done, fast and no
i, 8/29/14, Dave Click wrote:
Subject: Re: [RE-wrenches] Rapid shutdown questions
To: re-wrenches@lists.re-wrenches.org
Date: Friday, August 29, 2014, 12:08 PM
While I share Robin's optimism, I should also note the "NEC 2017 690.12
committee" referred to is not the code making pane
While I share Robin's optimism, I should also note the "NEC 2017 690.12
committee" referred to is not the code making panel. While it does have
(at least) one firefighter representative among a majority of PV
industry personnel, there's no guarantee that the Code Making Panel
approves this comm
Ops from Robin...
On 8/28/2014 11:00 PM, Robin Gudgel wrote:
Bob, I was mistaken about NEC2017 covering all PV systems. IT will
still just be for buildings.
On 8/28/2014 4:53 PM, b...@midnitesolar.com wrote:
>>>3) What about portable generators, and folks back feeding the grid
or
>>>3) What about portable generators, and folks back feeding the grid
or house with little to no protection at all.
Luckily, if the house is still connected to the grid when they try this,
the little generator will not be able to
power the neighborhood. Maybe not even the pole pig transforme
So this would make sense that this Rapid Shut down provision would cover
all generator backup systems too, not just solar.
Considering auto start backup generators have been around for many
decades, I have a few questions:
1) Does NEC 2014 require Rapid shutdown for all generator systems, or is
[Robin chiming in, below]
Dan, The 2014 690.12 is worded poorly. That is why there is so much
confusion. MidNite Solar is sitting on the NEC2017 690.12 committee.
There are a lot of smart people in this group. The 2017 version says ALL
PV SYSTEMS, not just on or in buildings. The 10 foot spac
Hi Mac, all;
Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ
stories yet. But look at 690.12 (1):
"Requirements for controlled conductors shall apply only to PV system
conductors of more than 5 ft in length inside a building, OR more than 10
ft from a PV array."
(my emphasis on
us by e-mail is deemed to have
>> accepted these risks. RGS Energy is not responsible for errors or omissions
>> in this message and denies any responsibility for any damage arising from
>> the use of e-mail. Any opinion and other statement contained in this
>> message an
, August 27, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rapid shutdown questions
Hi Will,
Yes I'm sure AHJ's will be all over the place for a while here in Colorado. To
clarify, is this a manual disconnect in the attic? If so, that is really
missing the whole idea of a rapi
d other statement contained in this
> message and any attachment are solely those of the author and do not
> necessarily represent those of the company.
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *M
those of the company.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Mac Lewis
Sent: Wednesday, August 27, 2014 8:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown questions
Hello wrenches,
I am still trying to wrap my head around how to comply with ra
Hello wrenches,
I am still trying to wrap my head around how to comply with rapid shutdown
in off-grid and hybrid situations. I've got a few questions that maybe you
can help with.
1. What is a (currently listed) rapid shutdown system that will
accommodate 8 strings? I know I can do this with