William,
It's my understanding the SMA Sunny Island inverters do this as well.
Dick Ratico
Solarwind Electric
--- You wrote:
Darryl:
There is a scenario in which problems occur: If your loads exceed the
generator capacity, the Outback system will fail. The Xantrex inverters
are superior in
Darryl:
There is a scenario in which problems occur: If your loads exceed the
generator capacity, the Outback system will fail. The Xantrex inverters
are superior in this scenario in that they will transition to invert mode
to synchronize with the generator and support the generator as long
I should have been a bit more clear about my application. I'm not
worried about battery charging rates or load percentage on the
generator. I've already determined that this size generator will
normally run at a good efficiency level. I am more concerned with the
quality, longevity, and enclosure.
On
Behalf Of Allan Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual
Outback Inverters
The Onan RS2 shown in the generators article in
ar.com
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters
Th
takes a lot of words to describe and decide what is the correct generator sizing.
Darryl
--- On Wed, 7/21/10, Mark Frye wrote:
From: Mark Frye
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters
To: "'RE-wrenches'"
Date: Wednesday, July 21, 2
more power
the Outback can reduce the charging rate until the AC load diminishes.
It takes a lot of words to describe and decide what is the correct generator
sizing.
Darryl
--- On Wed, 7/21/10, Mark Frye wrote:
> From: Mark Frye
> Subject: Re: [RE-wrenches] Propane Generator, Dual O
ts.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, July 21, 2010 11:21 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Propane Generator, Dual Outback Inverters
I'm looking for experiences/recommendations for a 15-20kW propane generator.
It would be going in a
I'm looking for experiences/recommendations for a 15-20kW propane
generator. It would be going in an off-grid system with dual Outback
3600W inverter/chargers. The excess capacity would power larger loads
than the inverters can handle. Fuel economy and harsh environment
performance are the top prio
9 matches