Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread solar1online
Solar 1 314 631 1094 -From: palumbo1...@gmail.com To: "RE-wrenches" Cc: Sent: 09-Jan-2018 21:19:00 +0000 Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem Thank you all for your help. Ray gets the gold star long distance diagnostics award as it

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread palumbo131m
Thank you all for your help. Ray gets the gold star long distance diagnostics award as it was simply a thin layer of ice underneath the air cleaner. I cleared that out and it started right up and ran in good shape. Dave Sent from my iPhone > On Jan 9, 2018, at 3:35 PM, Chris Mason wrote: > >

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread Chris Mason
If the unit is still under warranty, have any Generac dealer run through the diagnostics. The testing flow suggests rotor or stator problems, and there is a proscribed testing flow that needs to be performed. If it is determined to be a warranty issue, it will be fixed for you at no cost. If it is

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread John Blittersdorf
Dave, I had undervoltage on an eco-gen when the programming accidentally got changed to 240V when it is a 120V unit. John B. On Tue, Jan 9, 2018 at 5:13 AM, Darryl Thayer wrote: > Hello David, I have had that problem on other generators. > I have had similar problems not with an Eco gen but

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread Darryl Thayer
Hello David, I have had that problem on other generators. I have had similar problems not with an Eco gen but with a couple of other propane generator models. The problem occurs during cold weather. The problem was poor gas supply pressure and the problem was I could not convince anyone that was t

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread dan
ays the first to go'.. Good Luck. db Dan Brown Foxfire Energy Corp. Renewable Energy Systems (802)-483-2564 [1]www.Foxfire-Energy.com NABCEP #092907-44 Original Message Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem From: Ray <[2

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread Ray
-wrenches] GENERAC EcoGen 6kw problem Check to see if it’s programming matches its wired and expected voltage output configuration. Sent from my iPhone On Jan 8, 2018, at 6:13 PM, David Palumbo wrote: I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that starts quickly

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread David Palumbo
:30 PM To: RE-wrenches Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem Check to see if it’s programming matches its wired and expected voltage output configuration. Sent from my iPhone > On Jan 8, 2018, at 6:13 PM, David Palumbo wrote: > > I am troubleshooting a 6kw EcoG

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread maver...@mavericksolar.com
Check to see if it’s programming matches its wired and expected voltage output configuration. Sent from my iPhone > On Jan 8, 2018, at 6:13 PM, David Palumbo wrote: > > I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that > starts quickly > • but immediately shuts down

[RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread David Palumbo
I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that starts quickly • but immediately shuts down with an “Under Voltage” shutdown alarm • I can clear shutdown alarm and restart with same result. I tried this a few times with same result. One of the start attempts included a