Sent: Sunday, December 20, 2009 9:49 PM
To: gilliga...@gmail.com; 'RE-wrenches'
Subject: RE: [RE-wrenches] DC disconnect placement
Hello all,
While this may be excellent advice, I think it would be good to clarify that
this may apply primarily to grid tied systems.
I
enches-boun...@lists.re-wrenches.org] On Behalf Of Matt Lafferty
Sent: Sunday, December 20, 2009 4:10 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] DC disconnect placement
William,
Put the inverters at the array. Run the AC underground. If the AC feeder gets
dug up by some rowdy
Sent: Sunday, December 20, 2009 12:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC disconnect placement
Dick:
We are gong to install HU361 disconnects at the PV. Touch-safe fuse holders
are one way to apply disconnecting means rated at 600 VDC to a Sola Deck
device. Fusing at an array and G
to a dead short.
Cheers,
Matt Lafferty
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Sunday, December 20, 2009 11:02 AM
To: RE-wrenches
Subject: [RE-wrenches] DC disconnect placement
Friends
Bill.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Sunday, December 20, 2009 12:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC disconnect placement
Dick:
We are gong to install HU361 disconnects at t
I to agree it is nice to have a disconnect means at the pv array. I
worry that touch safe fuses may give some one the wrong idea as they are
not safe to open under load. they will catch on fire. I like the
combiner with disconnect idea and I know there is a Huge player in the
combiner market th
Dick:
We are gong to install HU361 disconnects at the PV. Touch-safe fuse holders
are one way to apply disconnecting means rated at 600 VDC to a Sola Deck
device. Fusing at an array and GFDI at an inverter do not de-energize PV
feeders. Combiner fuses, if required, protect only adjacent arra
ts.re-wrenches.org] On Behalf Of William
Miller
Sent: Sunday, December 20, 2009 2:02 PM
To: RE-wrenches
Subject: [RE-wrenches] DC disconnect placement
Friends:
I am embarking on a 10 Kw ground mount grid-tie installation. The client
prepared for this installation some time ago by stubbing a PVC co
William,
Not sure I understand how buried PV runs protected by touchsafe fuses in
combiner boxes at the array and GFCI protection at the inverters constitute a
fire hazard.
That's not saying I disagree with your disconnect here. I don't. If it was a 1kW
system, would you still install one? I would
Friends:
I am embarking on a 10 Kw ground mount grid-tie installation. The client
prepared for this installation some time ago by stubbing a PVC conduit
underground towards the future location of the PV array. Prior to
beginning this job, an excavation contractor intercepted the empty condui