I mean twice the Watts / Amp.
---
On 2021-08-03 10:13, drake.chamber...@redwoodalliance.org wrote:
Hi Brad,
The auto transformer should work just fine. You should get 4X the efficiency with 1/2 the current and twice the Watts / Volt. I don't know how much benefit is available from parallelin
Hi Brad,
The auto transformer should work just fine. You should get 4X the
efficiency with 1/2 the current and twice the Watts / Volt. I don't know
how much benefit is available from paralleling wires of different sizes;
it is not recommended practice of course.
If you find a source for those
The system currently has a 600 foot run of 2-2-4 aluminum from the service
to the house loads. The load is often only 120VAC which gives a large
voltage drop using only the #2 and #4 conductors. My thought was to install
an autotransformer at the load end so that the current runs through the #2
con