The system currently has a 600 foot run of 2-2-4 aluminum from the service to the house loads. The load is often only 120VAC which gives a large voltage drop using only the #2 and #4 conductors. My thought was to install an autotransformer at the load end so that the current runs through the #2 conductors at 240VAC for much less voltage drop. Are there any issues I should be looking at doing this? I’m thinking that to balance the legs a 4kVA autoformer would be adequate. The circuit is protected by 30A breakers both ends.
Second question is if I could reduce the voltage drop even more by taking the #4 and paralleling it to one of the #2 conductors. This would eliminate the neutral on the long run. I’m thinking that the autoformer could generate a new neutral for the load circuits. This is an older install so the neutral is already grounded to earth at both ends, there is no ground wire between the two such as would be required by code now. I know that code does not allow paralleling conductors smaller than 1/0 but I will disregard that in this case since it’s my own system. If anyone has one of the old AEE toroid autoformers you’d like to sell, or if you want one yourself we can do a bulk buy. Let me know off list. Thanks, Brad Bassett AEE Solar
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org