Re: [RE-wrenches] Outback quad stack X240 breaker tripping

2015-03-17 Thread Matt James
are imbalanced, one possible solution is to disconnect the neutral from the generator at the power system end. This presents a pure 240v load to the genset, which will force the currents to be balanced on both phases. Feel free to contact me directly if you have any problems or questions.

Re: [RE-wrenches] Outback AGS & eq

2015-02-13 Thread Matt James
Hi All, I confirmed that a Mate3 with 002.017.000 firmware or later will stop after an EQ cycle if the AGS gen control function is changed from Manual to Auto after the genny is started. It may also work with earlier firmware revs, but I only had a 2.17 rev close by for testing. Matt James

Re: [RE-wrenches] outback radian on 120v

2014-09-25 Thread Matt James
HI Jay, The Radian requires a 120/240 source in order to pass through AC power and charge the batteries. Hope this helps! Matt James Applications Engineering Manager OutBack Power Technologies Inc. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re