are imbalanced, one possible solution
is to disconnect the neutral from the generator at the power system end. This
presents a pure 240v load to the genset, which will force the currents to be
balanced on both phases.
Feel free to contact me directly if you have any problems or questions.
Hi All,
I confirmed that a Mate3 with 002.017.000 firmware or later will stop after an
EQ cycle if the AGS gen control function is changed from Manual to Auto after
the genny is started.
It may also work with earlier firmware revs, but I only had a 2.17 rev close by
for testing.
Matt James
HI Jay,
The Radian requires a 120/240 source in order to pass through AC power and
charge the batteries.
Hope this helps!
Matt James
Applications Engineering Manager
OutBack Power Technologies Inc.