Re: [RE-wrenches] Overpowered DC input

2025-01-07 Thread Jerry Shafer via RE-wrenches
Wrenches, Historically the older sma's would clip amps, l have programmed many at the request of the utility, l had one out of the box clipping as 10 watts rather than the 10 kW. it was nameplated as. Anyway its all in the voltage not the amps to worry about. Clipping may increase heat so keep them

Re: [RE-wrenches] Overpowered DC input

2025-01-07 Thread Blair May via RE-wrenches
How old r the modules? 1.5 + is not a problem, the fan will come on but the STC is not the NOC. w/ a new modules the PTC verses STC figures is~ 20- 30 less watts. These days we all seem to b replacing older modules that have lost some umph. We would always push the SBs 1.5 as a standard practice.

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread Jay via RE-wrenches
Hi BillGiven that the LBCO would happen probably without solar or limited anyway the fm-80 is going to read battery volt because no current. Sorry I confused the issue previously Just calibrate the fm-80 with no solar production and you should be fine. JayOn Jan 7, 2025, at 4:26 PM, Bill Battagin v

[RE-wrenches] Overpowered DC input

2025-01-07 Thread Bill Battagin via RE-wrenches
Another quandary.  The old SMA SBX000US transformer inverters would cost an arm and a leg to ship off (and returned from) somewhere to be fixed, if even fixable at a reasonable rate.  I found one online source that wanted $4K for one of these old timers, shipping not included. I was called to t

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread Bill Battagin via RE-wrenches
Looks like a lot of unknowns.  Another head-spinning idea.One method to my wanting to use the FM80 might be to set a LBCO voltage too high just to simulate a shutdown, have a fluke on the battery bus and another on the aux output, load the battery to drop battery voltage.  When to aux activ

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread jay via RE-wrenches
Hi Mac, yeah its confusing. As far as I know, the fndc only controls the FNDC functions. its own internal AUX, and AGS % which you can control through the inverter relay or the FNDC relay. All the other AUX relay functions are controlled by the device the AUX is in. But I could be mista

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread Mac Lewis via RE-wrenches
Hi Jay, Adding some nuance here, and I could be mistaken about all of the functions that get taken over by the FNDC voltage. When you calibrate the FNDC, it "shows" the voltage on the Mate as the FNDC voltage if there is an FNDC in the system. I also believe that it defaults to the FNDC voltage

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread Jay via RE-wrenches
Hi MacI’mGoing to disagree. The FNDC only provides its voltage it doesn’t populate to the other devices. You still have to set the inverter and CC separately, a poor design. Depends on which mate you’ve got where the fndc voltage is located. One reason I don’t like the CC voltage for aux control is

Re: [RE-wrenches] Alternate LVD shutdown

2025-01-07 Thread Mac Lewis via RE-wrenches
Hi Bill, Do you have a flexnet in the system? I assume that it wouldn't matter if the FM80 is calibrated but you will want the flexnet perfectly calibrated if you are using Lithium. It's a very annoying but worthwhile process. Don't drop the little nuts. Here is a paper on the procedure: http