Re: [RE-wrenches] Rectifier

2020-04-18 Thread Ray
When doing the volt drop calculation, be sure to correct for temperature, per the note after table 8, chapter 9 of the NEC. The table values default at 167 deg F (75 C).  An underground cable will be operating closer to earth temperature.   When I run volt drop for a 4/0 copper cable at 60 deg

Re: [RE-wrenches] Rectifier

2020-04-18 Thread Darryl Thayer
Hi Mac, There are a few questions like is it Al or Cu wire, What makes it unusable? for Voltage drop, I use Vd=2KIL/CMA for your case the unknown is the current. The installation of an inverter with grid support. Many inverters have this, you want a multimode inverter such as a Schneider, Outbac