William,
In the article you linked, directly after the image you included most
recently, John Wiles states "Unfortunately, we do not have a definition of
“PV system” in the Code."
I would have to disagree there. Article 100, Definitions includes:
"Photovoltaic (PV) System. The total components a
Greetings,
I have a customer whose ARE 110 voltage clamp has stopped working. I'm
looking for a work around. Has anyone been down this road before? If so,
I would like to hear what you've learned and maybe save myself some
mis-steps in the process. Many thanks!
--
Matt Sherald
PIMBY Energy,
The original question was w/r to:**/The source interconnection of one or
more inverters installed in one system shall be made at a dedicated
circuit breaker or fusible disconnecting means./
and whether one disconnect could be used to disconnect multiple
inverters. The inference as I read it wa
Hi Chris,
For string inverters, the OCPD is sized per 705.60(B) which will specify
the minimum breaker rating you need. Then, you can't go above the maximum
OCPD specified by the manufacturer. For most string inverters that I can
think of, this limits us to one breaker (OCPD) per inverter. I recal
Chris:
The 2014 code would require individual disconnecting means prior to
aggregation, i.e. an AC combiner. Therefore your scenario would not exist.
Wm
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Christopher Warfel
*Sent:* Wednesday, February 2
Larry, Wrenches:
I appreciate your questions and comments. I think there is a broader
question here: How do we differentiate between a perceived intent of the
Code authors versus the actual language they provide in the Code?
Many members of this forum have commented on the forum and to me o
I know I keep popping up on this, but 2014 makes no sense if it is
saying to connect multiple inverters to one disconnect. It would be
difficult and dangerous to take one out of service for any reason
including replacement. I would that that you'd have to shut down all the
inverters just to rep
William,
It seems this question needs to be addressed: What is the intended meaning of
“installed in one system” in 2014? If you have separate “systems”, they should
not be governed by 705.12. So, at what point does a “system” begin and end? PV
modules to the disconnect? ...to the load panel? .