Most 200A meter cans have a minimum wire size of #6. The Milbank K4977-EXT
tap connector might do the trick to get you down to #12 if your utility
will allow it:
http://www.milbankworks.com/blog/wp-content/uploads/2013/03/TapConnectors_6-13_Web.pdf
.
I think that it will work without a wire under
Daniel
What is the minimum size the lug will except
Jerry
On Fri, Sep 2, 2016 at 9:33 AM, Daniel Tittmann
wrote:
> wondering if anyone has a simple lug solution for a problem i found my
> self in.
> with out looking I used a meter socket for a REC meter that is not rated
> for #12 AWG wire. it
wondering if anyone has a simple lug solution for a problem i found my self
in.
with out looking I used a meter socket for a REC meter that is not rated
for #12 AWG wire. it is on a 20 breaker but wire size is too small for the
lugs. Is there a simple Lug solution that will pass muster or do I ne
Hi Tom,
Will you share the failures you had with the testing you did? How long ago was
the test? It looks to me like Rolls Battery has chosen FullRiver as their OEM
supplier for AGM batteries. Iām very sure they tested extensively and choose
carefully.
Thank you,
Larry Crutcher
Starlight Sol
Gary
A number of years ago I designed the back-up system for the Washington DC Metro
System communications in conjunction with Apollo Solar. After extensive testing
of both the Concorde and Full River brand batteries. We chose Concorde
SunXtender because of failures in the Full River during tes
I checked the math and it indeed seems like a rounding issue ā 20,000 W /
480 V / ā3 = 24.05626122 A
I wonder if the SMA tech support agent that Brian spoke with was just
reading the manual when they said it was 24.1 A. Regardless, it seems like
we would need to rely on the manufacturer to clari
Hello all,
I have 2 sets of Concorde Sun-Extender batts I installed in the one and only
Richard Perez' home about 4 years ago. One 12v pack and one 24v pack. No signs
of anything kinky. I try to Re-torque terminals every 1-2 years. I will
probably re-torque them again next week when I visit.
Hey Gary,
We have used those in about 10 systems. Our oldest bank of 2V is about 5 years.
As with all FullRiver batteries, no one has had any trouble.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Sep 1, 2016, at 8:08 PM, Gary Willett wrote:
Larry:
What is your experience wi