Could someone please explain the sequence of re setting a system with a Midnite
Birdhouse, disconnecting combiner, and battery disconnect module.
I mean, once the system is activated what is the correct sequence of re setting
and turning the equipment back on, whether AC power to the birdhouse i
Yes works fine no problems.
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Jay
Sent: July-25-16 2:33 PM
To: RE-wrenches
Subject: [RE-wrenches] Older XW with new XW accessories
I've got a customer with an older pair of XW 4048 invert
No issue I could see. I've done that exact same thing.
Thank you,
Maverick
Sent from an iPhone.
> On Jul 25, 2016, at 4:33 PM, Jay wrote:
>
> I've got a customer with an older pair of XW 4048 inverters and cc's.
>
> He would like to use the new web conext box, and probably the battery mete
I've got a customer with an older pair of XW 4048 inverters and cc's.
He would like to use the new web conext box, and probably the battery meter
with them.
Anybody know if this is possible?
Thanks
Jay
Peltz power.
___
List sponsored by Redwood Al
That wouldn't be a ground fault.
On Jul 25, 2016 9:01 AM, "Jason Szumlanski" <
ja...@floridasolardesigngroup.com> wrote:
> That's what the customer wanted, but even if I cut the leads short and
> terminated them, there would still be a risk of a ground fault to the
> module frame from water intru
Wrenches,
We have recently had a string of Solectria 3.8 failures. The commonality
to the failures seems to be a failed internal relay on the top part of the
inverter and we (and one customer) have witnessed brief arcing occur as
the inverter attempts to start up. In every instance we have seen
That's what the customer wanted, but even if I cut the leads short and
terminated them, there would still be a risk of a ground fault to the
module frame from water intrusion. In the end I was able to convince the
customer to remove it. We moved a module from the end to the middle where
this broken