Hi Jay;
Ah, its for load shedding. How come the max input amps setting doesn't
limit the total power drawn from the generator? That should throttle
back the charging rate to maintain full power thru to the loads.
Giving the batteries a 56 v for 5 min and dropping back to float
wouldn't const
Hi Ray,
I guess my answer is that its way easier to switch one button with easy access
than go deep into the menus and have to change 4 inverters.
This situation is a short term thing. In this case it is an issue as the
generator cannot handle both the chargers and the load. And he doesn’t wa
I have found the local Cummins rep to be very happy to set us up as a
dealer for their generators. We buy through Cummins Northwest in either
Missoula MT or Spokane WA. Last time I bought one I thought it was a bit
over $4k if you hit me up off-line I will forward you my sales reps
name and inf
Benn,
We’ve done it several ways including putting four 14 x 1.5” TYPE 17 screws
per attachment point through the metal and into the 1” x wood purlin. The
key is that the load path all the way down needs to be capable of handling
the worst case loads. So we had to check that too. Some racking
ma
August, et al;
If the purlins are only 1"x4" or 1"x6" or1"x anything, are you only relying
on the 1" purlin as the attachment point or are you hitting the vertical
trusses below the purlins?
We are working on a corrugated roof right now and using a Schletter roof
bracket. The name of it esc
If it's 240V single phase center tapped between two legs of a 480V delta
transformer, then one of the 240V legs *is* technically a neutral. What you
have is two 240V legs between two of three 480V phases. That said, if the
service from the utility is this type of 480/240V "split-phase," which
presu
If it's delta there is no neutral.
On Apr 29, 2016 12:40, "jay" wrote:
> HI Jerry and all,
>
> I’m sorry if I confused the issue.
> I haven’t seen this, I’m doing the research for a friend.
> It has been measured at numbers provided. 480 line to line, 240v line to
> neutral, 2 hots wires, not 3
I would use Everest Express rail pop riveted to every trapezoid, it will
add a lot of strength to the roofing. You may not bee able to get it any
more though.
On Apr 29, 2016 09:54, "frenergy" wrote:
> Recently, a customer had a metal roof (not standing seam) installed by a
> "handyman". Pretty
Look into the Versabracket. We get quite a lot of metal roofing installed
around here over existing shingles with horizontal 1x4 battens. Spacing is
usually 2', however.
Jason Szumlanski
On Fri, Apr 29, 2016 at 9:55 AM, frenergy wrote:
> Recently, a customer had a metal roof (not standing se
Hi Jay -Usually 408 delta will have 3 legs. See https://en.wikipedia.org/wiki/Three-phase_electric_powerUnlike Wye, the neutral is center tapped from the winding between two of the legs.The third is a hi leg or "stinger" leg that is 1.5 times the others voltage to neutral.Sounds like what you have
What's wrong with the chargers being on? Just set the charge settings
(absorb 56 v, and absorb time 5 minutes) fairly low. It will lightly
charge for a few minutes, and then go to float.
Just because your customer imagines this to be a problem, doesn't mean
it actually is. Its not going to hur
When the generator is auto started, the inverter's charger will be
enabled. After the generator is stopped, the inverter's charger will be
returned to the mode before the generator started. The logic is if you
are running the generator the Inverter's charger should be enabled. You
could lower t
I've seen a number of Eco Gen's go with no issues for a long time and 2
others blow all the oil out just as Drake noted. Rather worrisome!
Rich
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Drake
Sent: Friday, April 29, 2016 1:18 PM
To
The one and only EcoGen I installed blew out its
oil in within the first couple hours of running.
It severely damaged the engine. Generac did the
service and ultimately replaced the unit. It had
something to do with the two reservoirs and the hoses.
At 11:59 AM 4/29/2016, you wrote:
Wrenche
A 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
> -- next part --
> An HTML attachment was scrubbed...
> URL: <
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160429/7a62a058/attachment-0001.htm
> >
HI Jerry and all,
I’m sorry if I confused the issue.
I haven’t seen this, I’m doing the research for a friend.
It has been measured at numbers provided. 480 line to line, 240v line to
neutral, 2 hots wires, not 3.
The client has been told by 3 different installers that its impossible syste
Hi Bill,
What about installing unistrut to the roof on those attachment points, then
installing the racking to the unistrut?
jay
peltz power
> On Apr 29, 2016, at 6:55 AM, frenergy wrote:
>
> Recently, a customer had a metal roof (not standing seam) installed by a
> "handyman". Pretty clean
Dana,
Reaching back into my brain archives, having done a few projects with these
modules, I know that many, if not all, of these modules were rated for a
maximum system voltage of 48-volts. They can’t be used on higher voltage PV
arrays.
This was a budget version of their standard produ
Hi Bill,
It sounds like you’re talking about a purlin type setup – 4’ sounds a
little far apart but I guess that’s what you have to deal with. If you have
a corrugated metal roof, we’ve used S-5 CurruBrackets screwed through the
metal and into the purlins and then either run the solar rail up an
Hardy has been purchased by SW Prod.; they are in of PHX, AZ.
Great unit I agree, but 1 - not everyone is happy or comfortable with owning a
diesel & 2 - at elevation here in CO with –F° temps it is not always a good
choice without a warmed shed.
-
Hi Travis,
Can you recommend a good supplier for the Onan RV #HGJAB units?
Thanks,
Drake
At 10:59 PM 4/28/2016, Jordan Solar Sales wrote:
For off-grid generators I have found that the Onan propane RV units
like model #HGJAB are a great unit. (Onan is owned by Cummins, same
units as Cumm
Check out the hardy Diesel15 kW Perkins
It's available and integrated fuel tank single or double walland a whole bunch
of other goodies including autostart comes along with it
Like I mentioned in the last message the The folks I know they're in real cool
places put them in a small insulated buil
Panels in landscape mode with rails running peak to gutter?
On Apr 29, 2016 6:54 AM, "frenergy" wrote:
> Recently, a customer had a metal roof (not standing seam) installed by a
> "handyman". Pretty clean installation however for some reason he ran 1X6
> stringers across the roof on the 1/2" pl
Recently, a customer had a metal roof (not standing seam) installed by a
"handyman". Pretty clean installation however for some reason he ran
1X6 stringers across the roof on the 1/2" plywood deck spaced about
every 4 feet (as you go from ridge to eaves). Of course the roofing
screws are at
The newer Tripower STP3 can be configured for delta, but the 12000-24000
cannot. A step up transformer sounds like the way to go.
Best,
Garrison
Garrison Riegel
Solar Service Inc
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of jerrysgarage01
Sent: Thursda
Hi Jesse,
A regular visible blade lockable AC disconnect will satisfy our plan
checker’s concern. However, the utility does not require an AC disconnect
in our area for most residential applications so oftentimes we just use the
beaker as our disconnect. If we just use a back-fed breaker, he wan
Ditto here, if there is a 10-15KW, 1800 RPM water cooled generator out
there, please share. The EPA requirements & definitions have killed every
source I have had. An air cooled 3600 RPM generator is good for about
2000+/- hours before rebuild or replacement. Add to that the noise levels @
3600 RPM