Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
We were discussing remotely turning on and off the inverter itself like with the Outback's remote on/ off terminals. Magnum only has their remotes which aren't compatible with other systems. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Desig

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Jerry Shafer
Wrenches Bill said one thing we ALL need to listen to, that is untill someone asked it appears the renewable energy industry was not at the table. We need all to be asking why and asking for change, also asking the AHJ where it is and to clearify, sometimes thats all it takes. I bet that of who wa

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread b...@midnitesolar.com
On 3/15/2016 5:23 PM, Ray Walters wrote: Hi Brad; I think that remotely tripping the inverter might work with Outback, but definitely not with Magnum. (I checked with them today) Also, if the battery cables are more than 5 ft long, the rapid disconnect /might/ have to be closer to the batte

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
Hi Brad; I think that remotely tripping the inverter might work with Outback, but definitely not with Magnum. (I checked with them today) Also, if the battery cables are more than 5 ft long, the rapid disconnect /might/ have to be closer to the batteries. (/690.12 ...shall apply only to PV s

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
Hi Pat; HI Pat; No disrespect in either direction. I always appreciate everyone's views. Larry's Gigavac solenoid looks good too, but my read of 690.71 looks like I still need an OCPD within 5 ft of the batteries, as well. I'm already using substantial Midnite products for the actual "PV Circ

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Bradley Bassett
I've been promoting the use of the remote on/off terminals that are available in most inverters, which can be connected to the AUX in the Birdhouse. For a very minimum effort and cost, the inverter AC output would be shutdown when the rapid shutdown is activated. I think using the remote on/off te

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread August Goers
As a side note to this conversation, this brings up an advantage of the Tesla Powerwall battery – my understanding is that it will turn off immediately at the Powerwall battery when disconnected at the inverter. This is another nice benefit of having DC-to-DC conversion smarts in the Powerwall.

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread b...@midnitesolar.com
MidNite's Rapid Shutdown Sustems are UL listed. If you have any questions, please email Ryan at r...@midnitesolar.com. Ryan said we were actually having a webinar on this subject later this week, too. No solenoids so no night tare loss on the battery side or the PV side. *

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Starlight Solar Power Systems
This is from the spec sheet: "Hermetically sealed – UL listed: UL1604 for Class I & II, Div 2 and Class III for use in hazardous locations, IP67 for temporary water immersion for 30 min, IP69K for perssure washing, SAE J1171 - external ignition protection, and ISO8846 for protection against ign

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Patrick A. Shortell
Hi Ray Well you got me there I meant no disrespect to you personally. I think as a whole the code making panels do their best to keep up. If I missed some of the particulars Please excuse me. And I guess it would be more useful to offer a workable solution Maybe I've missed some of the details but

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
All right Larry, that's an actual start to a solution. My comments: 1) We already have had a solution for the array side using a Midnite Birdhouse and Midnite rapid disconnecting combiner box. (The /PV Circuit/ of the "/PV system circuit/" so I wasn't questioning that) 2) Who is the supplier

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread James Jefferson Jarvis
On 3/15/2016 3:57 PM, Starlight Solar Power Systems wrote: I thought this idea (attached) was a simple solution for array and battery rapid shutdown using a Classic controller and solenoids. The PV solenoids are 350 amp continuous @ 700 Vdc, and 400A @ 48 volts for the battery. Cost is about $120

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
So Pat, you stated "/There are simple ways to work around these issues/". Actually, the major off grid inverter manus do not have a solution for this ( Magnum, Outback, Exeltech, Schneider, SMA) Can you show us an example of a UL listed system that has multiple inverters (over 8 kW cont.), with

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Starlight Solar Power Systems
I thought this idea (attached) was a simple solution for array and battery rapid shutdown using a Classic controller and solenoids. The PV solenoids are 350 amp continuous @ 700 Vdc, and 400A @ 48 volts for the battery. Cost is about $120 each. Midnite told me than plan to implement the arc fa

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
Hi Bill; First, I didn't intend to "shoot the messenger". I have appreciated your many contributions to the PV industry, and enjoyed your education courses over the years. Thank You. However, 'PV system circuit' is not 'self defined' as you stated. By that same interpretation, a single GT sy

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Patrick Shortell
Dear List, Maybe it's an over simplistic opinion, but shouldnt all sources be disconnected rapidly in an emergency situation. We can always do better than what the code requires. I get frustrated when people go to the book, (and try to hide behind the text). instead of thinking through real life s

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread billbrooks7
Ray, I guess I have to step in after that acknowledgement. PV system circuit is a self-defined term and therefore cannot be defined unless you are going to develop a meaning that is different from the self-definition. It means ANY circuit in a PV system. This includes battery and stand-alone circu

[RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
Greetings Esteemed Wrenches: I've just heard back from our inspector here in Colorado, and we are still being required to disconnect the batteries under 690.12. No where in 690.12 are batteries mentioned, nor in the appropriate 690.71 section that deals with batteries. The entire reasoning b

Re: [RE-wrenches] Wire locator

2016-03-15 Thread Drake
I've rented pipe and cable locaters at tool rentals before. They can be tricky, but can also give good results. At 04:59 PM 3/14/2016, you wrote: We have a Schonstedt unit, works very well for electrical services. There has to be current in the cable to see it. Otherwise you can find data cables