I’m not sure if they are available everywhere as yet, I think they’re still
testing them with a few distributors. The compressors are not the Danfoss
they’re Tecumseh on the 48 volt units. Call me for more info on this.
Kind regards
Tom Duffy
Senior Solar Design Engineer
[Real-logo-X-195]
E-Mai
Oh, nice, thanks Tom! I wasn't aware of the 48v SunDanzer. Good units.
Dan Fink
Buckville Energy
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP / IREC / ISPQ Accredited Continuing Education Providers™
970.672.4342
On Fri, Nov 14, 2014 at 1:53 PM, T
Dan
Although I don’t understand the politics of this We have been selling the
SunDanzer 48 Volt 14 cu.ft. here in Panama, Central America, so as far as I
know there is a 48 volt something out there.
Kind regards
Tom Duffy
Senior Solar Design Engineer
[Real-logo-X-195]
E-Mail: t...@thesolar.biz
Garrison:
Are you sure you need a transformer to connect directly to the 3 phase? I
believe the system you refer to is an open-delta. We've installed the old
SB2500 units on open-delta before. This was before the neutral sensing
requirements, however. Many inverters have provisions for disa
Hi:
I came across this document related to battery venting and calculation of
the required vent hole size which was put out by Sonnenschein,
It's based on the EN 50272-2 standard. Perhaps it can be used to provide
some guidance for discussion with AHJ's
http://www.sonnenschein.org/PDF%20fil
Hello Wrenches,
In my area we end up installing a lot of systems on 240V 3Ph high leg
services. To allow for more inverter options (like TL that require a
neutral) it seems like using a transformer would a good idea, but it is hard
to justify the losses under load and especially 24/7 losses re
6 matches