Jeremy:
You are welcome, but credit belongs to Kent Osterberg.
wm
At 09:02 PM 12/30/2012, you wrote:
William,
They are using the 2011 code, so we should be good.
705.12D2 exception is a little confusing at first, but I got it.
Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
William,
They are using the 2011 code, so we should be good.
705.12D2 exception is a little confusing at first, but I got it.
Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine
List Address: RE-wrenche
Jeremy:
Bingo! You have discovered the hard truth of grid tie with battery point
of connection compliance (GTWB POC). Your inverter will through-transfer
up to 60 Amps (A), so to use all of that capability, you should feed it
with 60A. However, you are not allowed to feed the inverter with
Kent:
I do not have that document handy at this moment. Can you send the
citation, please?
Thanks,
William Miller
At 04:56 PM 12/30/2012, you wrote:
If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120%
rule for inverters with energy storage to allow for operation of lo
If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120%
rule for inverters with energy storage to allow for operation of loads.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882
On 12/30/2012 4:27 PM, Jeremy Rodriguez- All Solar Inc. wrote:
I'm
I'm concerned that the inspector will not allow a 60A back fed breaker in the
200A main panel as it exceeds the 120% rule
Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine
List Address: RE-wrenches@list
Jeremy:
The XW-6048 spec for maximum AC Input Current (maximum 75% imbalance
between L1-N, L2-N) is:
L-N: 41.2 AL-L: 27.5 A
So, with a Line to Neutral current of 41.2A x 1.25 = 51.5A or rounds up
to 60A 2-pole breaker.
This condition could occur in a grid-tied configuration when the
Ok, so 35A min., but what about maximum?
A 200A mains panels allows 120% max back feed correct?
Confused.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
-Original Message-
From: John Berdner
Date: Sun, 30 Dec 2012 23:54:17
To: allso...@scswifi.net;
RE-wrenches
Jeremy:
31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp
breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and
so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically b
Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are
connecting back to the load side of a 200A panel is this correct.
6000รท240=25X1.25=31.25A. We cannot exceed a 30A breaker? Help me understand
this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and