Ok, so 35A min., but what about maximum? A 200A mains panels allows 120% max back feed correct? Confused..... Jeremy All Solar Sent via BlackBerry. Sorry for typos and shorthand!
-----Original Message----- From: John Berdner <john.berd...@solaredge.com> Date: Sun, 30 Dec 2012 23:54:17 To: allso...@scswifi.net<allso...@scswifi.net>; RE-wrenches<re-wrenches@lists.re-wrenches.org> Subject: RE: [RE-wrenches] Point of Connection 705.12D2 Exception Jeremy: 31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp breaker would be the minimum size per Code. The inverter may have a higher "pass through rating" to support the loads and so is likely the reason a 60 Amp breaker is specified. The pass through rating is typically based on the size of the isolation relay and is usually higher than the inverter's continuous power rating. Best Regards, John Berdner General Manager, North America 3347 Gateway Boulevard, Fremont CA 94538 USA (*Please note of our new address.) T: 510.498.3201 ext 747 M: 530.277.4894 -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy Rodriguez- All Solar Inc. Sent: Sunday, December 30, 2012 10:35 AM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Point of Connection 705.12D2 Exception Wrenches, Since the XW6048 calls for a 60A breaker to feed the inverter input and we are connecting back to the load side of a 200A panel is this correct. 6000รท240=25X1.25=31.25A. We cannot exceed a 30A breaker? Help me understand this. Jeremy All Solar Sent via BlackBerry. Sorry for typos and shorthand! _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for the use of the individual or entity who is the intended recipient and may contain information that is privileged, confidential and exempt from disclosure or any type of use under applicable law. If the reader of this e-mail is not the intended recipient, or the employee, agent, or representative responsible for delivering the e-mail to the intended recipient, you are hereby notified that any dissemination, distribution, copying, or other use of this e-mail is strictly prohibited. If you have received this e-mail in error, please reply immediately to the sender. P Please think of the environment before printing this email _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org