Ok, so 35A min., but what about maximum?
A 200A mains panels allows 120% max back feed correct?
Confused.....
Jeremy
All Solar 
Sent via BlackBerry. Sorry for typos and shorthand!

-----Original Message-----
From: John Berdner <john.berd...@solaredge.com>
Date: Sun, 30 Dec 2012 23:54:17 
To: allso...@scswifi.net<allso...@scswifi.net>; 
RE-wrenches<re-wrenches@lists.re-wrenches.org>
Subject: RE: [RE-wrenches] Point of Connection 705.12D2 Exception

Jeremy:

31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp 
breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and 
so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically based on the size of the isolation relay 
and is usually higher than the inverter's continuous power rating.

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy 
Rodriguez- All Solar Inc.
Sent: Sunday, December 30, 2012 10:35 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception

Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are 
connecting back to the load side of a 200A panel is this correct. 
6000รท240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand 
this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to