Mick:
Do you have access to a dual trace oscilloscope? That is how I check phase
angle.
William
At 09:45 PM 4/7/2011, you wrote:
Hello, Mechanics~
I went to a distant "off grid" jobsite where my client has an
inverter/charger system set up for 120/240 60 hz system architecture.
While in
Hello, Mechanics~
I went to a distant "off grid" jobsite where my client has an
inverter/charger system set up for 120/240 60 hz system architecture. While
investigating some screwy charge behavior I clipped my "pretty good" Extech
clamp meter around the various AC wires from the generator, with t
the usual 208 3 phase is Y and not have high leg. sometimes you will measure
up
to 208 on the high leg of at Delta high leg to neutral. If it is Delta 3 phase
120-240 and a 200 about volt high leg, connect across the 240 volt legs, I e
that is across each phase they should be 240 each leg to
What is the best approach to interconnecting with a 208 volt 3-phase service
having a high leg? Small to medium sized PV systems.
Charlie Pickard
Aladdin Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
O
Daryl,
AEE has a corrugated
roof block that works pretty well. Penetrations are through the
ridges, where leaks are less likely, and they can be sealed with Butyl
tape. One draw back, same with the EJOT, is that the metal ridges will
rarely line up with support structure below. You'll need to
I have used hanger bolts on this exact roof several times. Filled the holes
with copious amounts of a good polyurethene sealant (vulkem) before driving
the hanger bolt, then built up with sealant around the hanger bolt base.
Haven't had any leaks, always tried to stay on the ribs, above the water
l
Interesting that it seems the industry is moving back to L-feet and sealant?
Always worked for many situations.
R. Walters
r...@solarray.com
Solar Engineer
On Apr 7, 2011, at 7:11 PM, Andrew Truitt wrote:
>
> Here's the VersaBracket option from S-5!:
>
> http://www.s-5.com/clamps/index_71
Daryl, I haven't done it but have heard of using "U" bolts from below to 2X
rafters. Think 8 inch long muffler clamp with a metal flat drilled plate on
the top, the bottom coated with sealant & L foot held down by nuts on top.
Pullout strength is unlimited and a sturdy metal plate to attach to plus
Daryl~ Take a look at the EJOT line of fasteners:
http://www.ejot.com/ejot.de/EJOT_Solarbefestiger_Bau_2009--2749,websiteLang__en.htm
These sort of look like a "hanger bolt" but they are machined to cram down
on a fat rubbery washer as they are tightened. EJOT is showing up in some of
the PV whol
Here's the VersaBracket option from S-5!:
http://www.s-5.com/clamps/index_71.cfm
For a brighter energy future,
Andrew Truitt
Principal
Truitt Renewable Energy Consulting
NABCEP Certified PV Installer™ (ID# 032407-66)
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713
[image: 24
I have been involved with two installs, They are working great, they have dual
inputs and the broadest MPPT range of any inverter I have seen. I have had no
failure problems, and I have a friend that has experience with several and he
reports no problems.
They are ungrounded so you have to
In addition to David's insight, I would like to also offer this link for the
manual:
http://www.sma-america.com/en_US/service/downloads.html
If you click on the "Archive" tab, documentation is available for all
out-of-production units.
Also, http://www.SMA.de sometimes may have info that the U
Hi Daryl,
I have drilled a small pilot hole, put plenty of sealant around it, then lag
through it with what ever foot you are using.
I don't think the cost of flashing around each foot with a rubber boot and 15
screws is any better but its sure more costly in time and money.
jay peltz power
Hi all. Does anyone have any experience with the Power One Aurora
grid-tied inverters? Any comments on the failure rate for inverters
manufactured in the last year or two?
Thanks.
Bruce Leininger
PV System Designer
GRID Alternatives
-
1171 Ocean Av
The Code back then was a little vague back then and I am not sure it has
been improved.
First, there needs to be a DC disconnect just before or just after
penetrating the building shell. Most AHJ allowed us to place this disconnect
in the attic within reach of the access door. Once we needed to pl
338.10(B)(4)(b) also kicks you over to 225 I... like 225.12+14- which kicks over to Table 230.51C.. maybe? (I'd do a messenger ground).Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: Re: [RE-wre
690.31(E), requiring metallic raceways or enclosures for DC circuits inside
the building was introduced in the 2005 NEC. Depending on when the 2005 NEC
was adopted by your local authority, it may or may not have been required at
the time of the installation.
-Hans
_
From: re-wrenches-b
Maybe check out 396?Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: [RE-wrenches] Conductor supporting requirements
From: Andrew Truitt
Date: Thu, April 07, 2011 1:39 pm
To:
Hi folks
Was wondering- does anyone know back in 2005, if it was permissible to run DC
conductors from the roof, through the home to the inverter location, inside the
house, per the NEC?
ThanksÂ
Keith Cronin___
List sponsored by Home Power magazine
Does anyone have experience mounting arrays on barns with 24" wide
galvanized roofing (not standing seam)? It is flat, not corrugated, but
has an overlapping edge on either side. It's pretty much a standard on
barn roofs around here, but I hesitate to penetrate any metal roof. How
have others dealt
Vermont has a "Group Net Metering" program that permits any individual
rate payers on the same utility to create a net metered array and have the
utility credit each members account according to a formal legal agreement.
Legislation requires that all utilities in the state are required to
allow an
This is a great topic for discussion on the RE-Markets list, where there are
several more policy-oriented folks than here. I am cc'ing that address in this
reply, so let's move the discussion there.
Community solar is an important, up-and-coming thing. Specially for folks that
don't have solar
I believe Massachusetts has this, which is called "community net metering".
New York State does not allow it, but a bill is in the assembly and senate this
session called "virtual net metering" whereby a single customer with multiple
meters can interconnect to one and apply excess generation cr
Washington State has a very good program which I believe is a kind of FIT
Community solar thing that pays over $1.00/kW generated.
Andrew Koyaanisqatsi
President
Solar Energy Solutions, Inc.
Since 1987,
Moving Portland and Beyond
to an Environmentally Sustainable Future.
503-238-4502
www.solar
Larry, et al,
The State of Maryland is working on legislation to enable such "virtual" net
metering arrangements but it is not here yet. It is a wonderful idea as you
can imagine new sub-divisions being built with one lot set aside for a large
array for the community.
We set up a group of local
If you have a muni then it's possible, but I'd guess that with most
investor-owned utilities they'd just laugh in your face. There are a few
utilites out there that have done this- I think that Portland, OR and
Seattle have this and we're working on it here in Orlando too.
These links should h
wrenches.
I have had several inquires into this possible scenario. anybody have
any experience doing this with their local utility?
several families in a neighborhood or community invest together to put
up a solar array either on an existing building that has excellent
solar access or a
338.10(B)(4)(b) says to support in accordance with 334.30:
334.30 Securing and Supporting.
Nonmetallic-sheathed cable shall be supported and secured by staples,
cable ties, straps, hangers, or similar fittings designed and installed
so as not to damage the cable, at intervals not exceeding 1.4
Does anyone know the maximum support spacing for conductors in free air and
what code section addresses it? I'm thinking of USE-2 or PV Wire being run
in loop hangars along purlins under an array.
Thanks in advance!
For a brighter energy future,
Andrew Truitt
Principal
Truitt Renewable Energy
Jesse,
Here is one more thing to look at. I have 3 SMA 1800 W inverters on my
house and had a very similar problem when I installed them. They are
very sensitive to AC voltage. Mine would turn off at 128 VAC. My
utility voltage is 125 per leg and because of voltage "drop" in a log
run of w
Mike,
I approached it as if the batteries where installed in a UPS system. What
constant float voltage would the batteries be charged at during grid-up, so
they would be ready for grid-down?
I would use 53.2V for Float and for Sell.
I also recommend to use software on the inverter to automatic
Trying to tweak a couple of battery based grid-tie systems.Trying to
maximize sell back without frying or draining the batteries. Have gotten
various opinions from manufacturer's techs, so why not a few more..
Concord AGM's set now as follows:
Bulk = 57.2v
float = 53.2v
sell = 52v
It is my u