Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Ryan LeBlanc
Steven, A Line Side Tap, by nature, allows us 100% of the Service Entrance Conductor Ampacity. This typically ~equals Main Breaker rating, but is regardless of the Main Breaker rating or size of Loads, it's about the conductor. NEC recognizes that our systems produce power, not draw it, so downs

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread penobscotsolar
I saw the fault "high ac input voltage" at least three times. I changed out the boards in the inverter TWICE, both times freebies from OutBack. I checked battery spec. grav., programmed it and re-programmed it, talked ad nauseum on the phone with tech supportnothing. It was OutBack tech support

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread Jeff Oldham
If you only need to log V, A and Hz (for this need anyway) you would do fine with the Fluke 289. I have one and love it. It will download to a computer too with FlukeView Forms via the IR port and interface cable (comes with FlukeView). This is a VERY fast meter and will capture anything that I

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread R Ray Walters
I've been considering a Fluke 345 for some time http://www.davis.com/catalog/product_view.asp?sku=2000338&pfx= It does data logging of power issues,and is very easy to carry around and work with (basically a clamp on meter with electrodes too) Do you think that would work? R. Walters r...@solar

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread R Ray Walters
What faults were you seeing when it wouldn't sell? Was grid voltage or frequency off? Or was it power factor issue? I might need some technical ammo to persuade the Utility into swapping their transformer. R. Walters r...@solarray.com Solar Engineer On Mar 31, 2010, at 1:32 PM, penobscotso.

Re: [RE-wrenches] Fwd: Outback Grid Problems

2010-03-31 Thread R Ray Walters
Boy I appreciate the many replies on this. To answer your curiosity,Kirpal, the customer lived off grid originally, brought in the grid after 5 years, but only used it as backup with his previous SW system. Now he likes to play with it, as he's also an EE. (He likes to cycle the batteries occasi

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread R Ray Walters
I suspect our performance issues are software related as well. Obviously Outback didn't optimize performance of their inverters for such a large battery. It would be nice to be able to understand and adjust some of those back door parameters, though. We've learned more about the problem: it appe

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
Hans, There's a backup load panel that some house loads are transferred to that's fed from the 60A line side tap. Under normal operation they are fed from the PV with the remaining power coming from the line side tap off from grid. To be thorough, one would have to make sure that the backup l

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread August Goers
Nick – It would be great if a load exception could be made but I’ve never heard of it. Do you have any references to the code? -August August Goers Luminalt Energy Corporation O: 415.564.7652 M: 415.559.1525 F: 650.244.9167 aug...@luminalt.com From: re-wrenches-boun...@lists.re-wrenches.org [

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread penobscotsolar
Ray, Believe me when I say I have gone through all the exercises described so far by our esteemed colleagues. I think you will find the problem is with the customers transformer. I continue to make impressive amounts of kwh since the swap out last week. Daryl > Battery bank is in great shape,

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Nick Soleil
I feel confident that the load will not be over 80 Amps at any time, and therefore do not think that a service upgrade is necessary. If the load is increased in the future (as in any situation,) the panel may need to be upgraded in the future. By 'legal,' I assume you mean that it is appro

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread Randy Brooks
Ray, The only fault warning we got was the batteries (a 48v, 1,000 amp hr HuP) were boiling and using a lot of water, and expected power production was down. OutBack said this problem was corrected with new software. The system was installed in 11/2005 and the inverters replaced in spri

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Hans Frederickson
Steven, I don't think the 60A disconnect for the line-side tap would qualify as part of the required 100A rating for the residential service. You aren't using it to supply the house loads. Unless I'm missing something, your proposal limits the residential service load to only 60A. I suppose you cou

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
230.80 "Where the service disconnecting means consists of more than one switch or circuit breaker, as permitted by 230.71, the combined ratings of all the switches or circuit breakers used shall not be less than the rating required by 230.79" Steven Lawrence

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread R Ray Walters
Ventilated, but small enclosure. Definitely a possibility to consider. What fault warnings were you getting? Thanks, R. Walters r...@solarray.com Solar Engineer On Mar 30, 2010, at 5:58 PM, Randy Brooks wrote: > Ray, > > Is the inverter in a ventilated space? We had a similar problem with

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread R Ray Walters
Battery bank is in great shape, is brand new HUP set. Thanks, R. Walters r...@solarray.com Solar Engineer On Mar 31, 2010, at 6:19 AM, t...@hughes.net wrote: > Ask the customer to ck the cells for bubbling during the charging period to > make sure the cells all are good OR Isolate the batte

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Hans Frederickson
Anything less than a 100A main is a no-go a for residential service: NEC 230.79(C): "For a one-family dwelling, the service disconnecting means shall have a rating of not less than 100 amperes, 3-wire." Also, I don't think any AHJ is going to accept a load calculation in lieu of proper bus sizing

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Steven Lawrence
Why can't you do a line side tap and downsize the main breaker? Use a 60A main disconnect for the line side tap, and use a 60A main breaker for the service panel. That's similar to what I did except I downsized the 200A main to a 150A. This also allowed a manual interlock kit in the main servi

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Eric Andrews
We recommend to the customer to upgrade their service if it's not adequate (old/outdated/too small). In the grand scheme of things, that's a small add-on. Whenever there's a questionable interconnect, it's always prudent to get a pre-approval from your AHJ and your utility. A supply side tap may

Re: [RE-wrenches] xantrex xw experiment

2010-03-31 Thread Phil Undercuffler
Nick, The answer would be technically yes, but with limitations and I'd question whether there would be any benefits, only downsides. To elaborate -- yes it's possible to install two XWs on two different batteries, using two different arrays and charging sources, but sharing the same AC grid and

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-31 Thread Nick Soleil
Downsize the main breaker? I would if I could, but the customer only has 100 Amps now, and the solar is fed with two breakers, a 30A and a 40A. So to be under 120Amps, I would have to size the main to 50 Amps, which may be problematic. I can also do the line side tap, but had heard tha

Re: [RE-wrenches] xantrex xw experiment

2010-03-31 Thread jay peltz
Hi Nick, I'm curious why the two banks of batteries? jay peltz power On Mar 30, 2010, at 10:58 PM, Nick Vida wrote: > Hi wrenches, > > I am looking at the xantrex XW system with 2 inverters, and I asked their > tech support if it is possible to have 2 inverters synced to the same grid > and

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread tump
Ask the customer to ck the cells for bubbling during the charging period to make sure the cells all are good OR Isolate the battery banks to make sure there isn't a dead cell the OBs are trying to charge. BB1 one day, BB2 the next & so on. Sent via BlackBerry by AT&T -Original Message-

Re: [RE-wrenches] Outback Grid Problems

2010-03-31 Thread tump
I have a company that will rent a Fluke power logger 1735 for ~ $300/ month. I have been using one to measure just this issue. I found the unit was easy to use + all the data logged can be downloaded. Logging can be as short as 1/2 second to 40 hours. Ck out what one can log, it is quite a bit

[RE-wrenches] ground fault issues

2010-03-31 Thread bob
Has anyone had any experience with a Magnum 4024 inverter (sine wave) and breaker box mounted ground fault breakers? A customers fellow just wired a ground fault outlet and it flashes on and off with the inverter on, not in sleep mode. I don't know if it's wired correctly or the brand but th