Why can't you do a line side tap and downsize the main breaker? Use a 60A main disconnect for the line side tap, and use a 60A main breaker for the service panel. That's similar to what I did except I downsized the 200A main to a 150A. This also allowed a manual interlock kit in the main service panel that can be fed from the backup load panel.
Steven Lawrence ______________________________________________________ Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT) From: Nick Soleil <nicksoleilso...@yahoo.com> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection Message-ID: <342120.66732...@web44904.mail.sp1.yahoo.com> Content-Type: text/plain; charset="us-ascii" Downsize the main breaker? I would if I could, but the customer only has 100 Amps now, and the solar is fed with two breakers, a 30A and a 40A. So to be under 120Amps, I would have to size the main to 50 Amps, which may be problematic. I can also do the line side tap, but had heard that a load analysis may be accepted instead. The loads of the house will never use more than 100 Amps. I am wondering if any codes or white papers detail that option. Nick Soleil Project Manager Advanced Alternative Energy Solutions, LLC PO Box 657 Petaluma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax: 707-769-9037 _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org