Why can't you do a line side tap and downsize the main breaker?  Use a 60A main 
disconnect for the line side tap, and use a 60A main breaker for the service 
panel.  That's similar to what I did except I downsized the 200A main to a 
150A. This also allowed a manual interlock kit in the main service panel that 
can be fed from the backup load panel.  

Steven Lawrence

______________________________________________________

Date: Wed, 31 Mar 2010 08:13:10 -0700 (PDT)
From: Nick Soleil <nicksoleilso...@yahoo.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Supply Side Tap Overcurrent Protection
Message-ID: <342120.66732...@web44904.mail.sp1.yahoo.com>
Content-Type: text/plain; charset="us-ascii"

    Downsize the main breaker?  I would if I could, but the customer only has 
100 Amps now, and the solar is fed with two breakers, a 30A and a 40A.  So to 
be under 120Amps, I would have to size the main to 50 Amps, which may be 
problematic.
    I can also do the line side tap, but had heard that a load analysis may be 
accepted instead.  The loads of the house will never use more than 100 Amps.  I 
am wondering if any codes or white papers detail that option.  

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to