William,
Congratulations on an elegant solution and thanks for following up.
It's always of great interest to hear how these things work out.
I know some AHJs can be obstructive or difficult to work with, but IMHO
the vast majority are more than willing to work with you, to arrive at a
good d
Mark,
The readily accessible disconnect at the inverter is all that is necessary
according to the code. There may be practical reasons for additional
disconnects, but if the system has no combiner box, or the combiner is at
the inverter, only the disconnect at the inverter is required.
Bill
Marco,
My only comment is the 3 phase units are a long lead time item. Fronius
expects to catch up to demand by end of Q1 2010.
Carl
SunRock Solar
On Thu, Dec 17, 2009 at 6:55 PM, Marco Mangelsdorf wrote:
> I have yet to install a Fronius IG Plus inverter. Looking through the
> manual I’m t
I was once told that the best collector used black chrome plated on bright nickel.
This combination absorbs heat well, with the advantage of not letting the heat back out.
Sort of a thermal "diode" of sorts.
I have no data, but I believe "good" collectors radiate less than they collect.
Mark
Mark:
If it were me, I'd put a disconnect prior to entry to the building. How
are you going to service the connections without a disconnecting means?
William Miller
At 03:24 PM 12/18/2009, you wrote:
Hello there,
Due to a lot of concrete and asphalt, we are forced to run our PV source
cir
Hi there gang,
Just to say that IMHO solar thermal panels will radiate quite a bit less
than they collect, someone must have some data on this ??
Have a great Christmas.
Carl Emerson
Free Power Ltd.
Web www.freepower.co.nz
_
From: re-wrenches-boun...@lists.re-wrenches.o
Well that wasn't supposed to go out to the masses but...
So happy holidays anyway.
Jim Duncan
- Original Message -
From: North Texas Renewable Energy Inc
To: RE-wrenches
Sent: Friday, December 18, 2009 8:26 PM
Subject: Re: [RE-wrenches] Solar System Certification
William
Mark --
It doesn't sound like your crawl-space run is 'readily accessible' either.
Could you put a DC disconnect on the exterior before you go inside?
Rebecca Lundberg
Powefully Green, Minnesota
---
>
> Message: 1
> Date: Fri, 18 Dec 2009 16:24:30 -0700
> From:
William
I'd be interested in including similar PE fee language in my proposals. If
you'd send that I would appreciate it.
I have only experienced a similar requirement once. In 2006 I was ordered to
include a PE report, to local bldg. code enforcement, on a fairly typical
residential PV install
Hello there,
Due to a lot of concrete and asphalt, we are forced to run our PV source
circuits in through one exterior wall, through a crawl space and out through
the opposite exterior wall to our inverter and disconnect. We will be using
EMT and will not be making any stops while inside the bui
Dick:
Just to follow up, below is the reply I received from the inspector when I
asked for clarification. I had asked for clarification because I admit
ignorance to this section and I wanted to formulate a good response on the
first attempt:
There must be a main disconnect for panel C in th
Brian:
I looked up the Municipal Codes
(http://www.ci.yorba-linda.ca.us/~ci26/how-do-i/get/get-city-codes) and
this requirement is right in there. I hope you have a provision in your
contract that allows for additional billing for unanticipated engineering
fees. Everyone should. If you nee
In terms of technique, the easiest way to accomplish this is to plumb a
valve in parallel with the systems' check valve, and have the customer open
it when nighttime diversion is necessary (middle of summer, customer on
vacation, no draw on system, etc). Unless the piping size or path limits it,
he
I am curious if any of you have had to deal with this issue before.
The following is an item we got back from the City of Yorba Linda for a Plan
Check correction:
All electrical solar systems shall be tested and approved by a California
Registered Electrical Engineer. The engineer shall f