[RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Kirk Herander via RE-wrenches
Hello All,
.
I have a Radian 8048 system in service for over 10 years now. It sold back
quite normally until the last several months -3.- FM60 CC's are set to grid
tie mode and  viewable and programmed from the Mate3s / OpticsRE. This
issue loosely correlates to replacing one of the CCs several months ago.

Trouble is all -3- charge controllers are almost always in a float mode.
The radian does sell, but at a small KW compared to what it used to before
the frequent float mode started popping up. If I remember correctly,
ideally the CCs should always be in bulk charge when sellback occurs.

I have the CC and inverter charger float set to about 1 vdc higher then the
inverter's sell volts, as I believe was recommended way back when. Hard to
understand what changed, but something did. I've checked the relevant
setpoints many times and can't find anything obviously amiss.

Does a sell mode tech note paper exist still for the Radian system? Did it
ever? Any ideas would be greatly appreciated.




-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Foxfire Energy via RE-wrenches
I had a similar problem a while back and it turned out to be the FNDC calling 
the shots.. Unplug the FNDC (if you’re using one).. see what happens.
db

Sent from my iPhone

On Aug 18, 2024, at 1:12 PM, Kirk Herander via RE-wrenches 
 wrote:


Hello All,
.
I have a Radian 8048 system in service for over 10 years now. It sold back 
quite normally until the last several months -3.- FM60 CC's are set to grid tie 
mode and  viewable and programmed from the Mate3s / OpticsRE. This issue 
loosely correlates to replacing one of the CCs several months ago.

Trouble is all -3- charge controllers are almost always in a float mode. The 
radian does sell, but at a small KW compared to what it used to before the 
frequent float mode started popping up. If I remember correctly, ideally the 
CCs should always be in bulk charge when sellback occurs.

I have the CC and inverter charger float set to about 1 vdc higher then the 
inverter's sell volts, as I believe was recommended way back when. Hard to 
understand what changed, but something did. I've checked the relevant setpoints 
many times and can't find anything obviously amiss.

Does a sell mode tech note paper exist still for the Radian system? Did it 
ever? Any ideas would be greatly appreciated.




--
Kirk Herander / kirkh@vermont.solar
Owner|Principal, VT Solar, LLC
Celebrating our 33st Anniversary 1991-2024!!
dba Vermont Solar Engineering
802.559.1225
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Jay via RE-wrenches
There is a setting called FLEXnet dc advanced control. Default is YI always set it to NPg 128 in my manual. JayOn Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches  wrote:Hello All,. I have a Radian 8048 system in service for over 10 years now. It sold back quite normally until the last several months -3.- FM60 CC's are set to grid tie mode and  viewable and programmed from the Mate3s / OpticsRE. This issue loosely correlates to replacing one of the CCs several months ago.Trouble is all -3- charge controllers are almost always in a float mode. The radian does sell, but at a small KW compared to what it used to before the frequent float mode started popping up. If I remember correctly, ideally the CCs should always be in bulk charge when sellback occurs.I have the CC and inverter charger float set to about 1 vdc higher then the inverter's sell volts, as I believe was recommended way back when. Hard to understand what changed, but something did. I've checked the relevant setpoints many times and can't find anything obviously amiss.Does a sell mode tech note paper exist still for the Radian system? Did it ever? Any ideas would be greatly appreciated.-- Kirk Herander / kirkh@vermont.solarOwner|Principal, VT Solar, LLCCelebrating our 33st Anniversary 1991-2024!!dba Vermont Solar Engineering802.559.1225
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Nick Lucchese via RE-wrenches
You're observing this on all three controllers or is the reduced sell back
off by a factor that would correlate to the newest controller you swapped?

Did you calibrate the new controller while the PV breakers were all off? I
still come across new FM80's that require utilizing the entire .5vdc margin
to match my Fluke.

Though it's not a solution can you temporarily raise the bulk setpoints of
all three to verify expected outputs?

It does seem like there was a document on proper sell back settings
somewhere.

Good luck, Nick


On Sun, Aug 18, 2024 at 10:11 AM Kirk Herander via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hello All,
> .
> I have a Radian 8048 system in service for over 10 years now. It sold back
> quite normally until the last several months -3.- FM60 CC's are set to grid
> tie mode and  viewable and programmed from the Mate3s / OpticsRE. This
> issue loosely correlates to replacing one of the CCs several months ago.
>
> Trouble is all -3- charge controllers are almost always in a float mode.
> The radian does sell, but at a small KW compared to what it used to before
> the frequent float mode started popping up. If I remember correctly,
> ideally the CCs should always be in bulk charge when sellback occurs.
>
> I have the CC and inverter charger float set to about 1 vdc higher then
> the inverter's sell volts, as I believe was recommended way back when. Hard
> to understand what changed, but something did. I've checked the relevant
> setpoints many times and can't find anything obviously amiss.
>
> Does a sell mode tech note paper exist still for the Radian system? Did it
> ever? Any ideas would be greatly appreciated.
>
>
>
>
> --
>
> *Kirk Herander / **kirkh@vermont.solar *
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 33st Anniversary 1991-2024!!*
>
> dba Vermont Solar Engineering
>
> 802.559.1225
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Kirk Herander via RE-wrenches
Looks like its only programmable directly on the Mate3s, not in optics RE.
Or maybe I haven;t found it yet.

On Sun, Aug 18, 2024 at 3:22 PM Jay  wrote:

> There is a setting called
>
> FLEXnet dc advanced control.
>
> Default is Y
>
> I always set it to N
>
> Pg 128 in my manual.
>
> Jay
>
> On Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
> Hello All,
> .
> I have a Radian 8048 system in service for over 10 years now. It sold back
> quite normally until the last several months -3.- FM60 CC's are set to grid
> tie mode and  viewable and programmed from the Mate3s / OpticsRE. This
> issue loosely correlates to replacing one of the CCs several months ago.
>
> Trouble is all -3- charge controllers are almost always in a float mode.
> The radian does sell, but at a small KW compared to what it used to before
> the frequent float mode started popping up. If I remember correctly,
> ideally the CCs should always be in bulk charge when sellback occurs.
>
> I have the CC and inverter charger float set to about 1 vdc higher then
> the inverter's sell volts, as I believe was recommended way back when. Hard
> to understand what changed, but something did. I've checked the relevant
> setpoints many times and can't find anything obviously amiss.
>
> Does a sell mode tech note paper exist still for the Radian system? Did it
> ever? Any ideas would be greatly appreciated.
>
>
>
>
> --
>
> *Kirk Herander / **kirkh@vermont.solar *
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 33st Anniversary 1991-2024!!*
>
> dba Vermont Solar Engineering
>
> 802.559.1225
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Jay via RE-wrenches
One other thing that has worked for weird issues is a full factory reset of everything. JayOn Aug 18, 2024, at 4:18 PM, Maverick Brown  wrote:On OpticsRE go to devices, Mate3S, Global Charge. Disable everything there and for good measure also set the Maximum Battery Charge to generously large number. Also, if you recently upgraded to Inverter software 1.6.63 or later, you have to do some procedure to edit the maximum sell currentupgrading_1_6_63_app_notePDF Document · 200 KBThank you,MaverickMaverick BrownOff-Grid Solar Commander since 2006Maverick Solar Enterprises, Inc. • Solar Commander Remote Power • SunFlow Systems Cathodic Protection maver...@mavericksolar.com512-460-9825On Aug 18, 2024, at 3:59 PM, Kirk Herander via RE-wrenches  wrote:Looks like its only programmable directly on the Mate3s, not in optics RE. Or maybe I haven;t found it yet.On Sun, Aug 18, 2024 at 3:22 PM Jay  wrote:There is a setting called FLEXnet dc advanced control. Default is YI always set it to NPg 128 in my manual. JayOn Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches  wrote:Hello All,. I have a Radian 8048 system in service for over 10 years now. It sold back quite normally until the last several months -3.- FM60 CC's are set to grid tie mode and  viewable and programmed from the Mate3s / OpticsRE. This issue loosely correlates to replacing one of the CCs several months ago.Trouble is all -3- charge controllers are almost always in a float mode. The radian does sell, but at a small KW compared to what it used to before the frequent float mode started popping up. If I remember correctly, ideally the CCs should always be in bulk charge when sellback occurs.I have the CC and inverter charger float set to about 1 vdc higher then the inverter's sell volts, as I believe was recommended way back when. Hard to understand what changed, but something did. I've checked the relevant setpoints many times and can't find anything obviously amiss.Does a sell mode tech note paper exist still for the Radian system? Did it ever? Any ideas would be greatly appreciated.-- Kirk Herander / kirkh@vermont.solarOwner|Principal, VT Solar, LLCCelebrating our 33st Anniversary 1991-2024!!dba Vermont Solar Engineering802.559.1225
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org-- Kirk Herander / kirkh@vermont.solarOwner|Principal, VT Solar, LLCCelebrating our 33st Anniversary 1991-2024!!dba Vermont Solar Engineering802.559.1225
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] OB Radian / FM60 grid tie mystery

2024-08-18 Thread Dave Angelini Offgrid Solar via RE-wrenches
You are all the Outaback wrenches but with Schneider before you reset 
the defaults, you should just do a complete DC power down.  Just in case 
it is a stuck bit in config.


Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [2]https://offgridsolar1.com/ [3]  [2]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2024-08-18 4:20 pm, Jay via RE-wrenches wrote:

One other thing that has worked for weird issues is a full factory 
reset of everything.


Jay

On Aug 18, 2024, at 4:18 PM, Maverick Brown 
 wrote:


On OpticsRE go to devices, Mate3S, Global Charge. Disable everything 
there and for good measure also set the Maximum Battery Charge to 
generously large number.


Also, if you recently upgraded to Inverter software 1.6.63 or later, 
you have to do some procedure to edit the maximum sell current




upgrading_1_6_63_app_note [1]
PDF Document · 200 KB [1]

Thank you,

Maverick

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
* Solar Commander Remote Power
* SunFlow Systems Cathodic Protection
maver...@mavericksolar.com
512-460-9825

On Aug 18, 2024, at 3:59 PM, Kirk Herander via RE-wrenches 
 wrote:


Looks like its only programmable directly on the Mate3s, not in optics 
RE. Or maybe I haven;t found it yet.


On Sun, Aug 18, 2024 at 3:22 PM Jay  wrote:

There is a setting called

FLEXnet dc advanced control.

Default is Y

I always set it to N

Pg 128 in my manual.

Jay

On Aug 18, 2024, at 11:11 AM, Kirk Herander via RE-wrenches 
 wrote:


Hello All,
.
I have a Radian 8048 system in service for over 10 years now. It sold 
back quite normally until the last several months -3.- FM60 CC's are 
set to grid tie mode and  viewable and programmed from the Mate3s / 
OpticsRE. This issue loosely correlates to replacing one of the CCs 
several months ago.


Trouble is all -3- charge controllers are almost always in a float 
mode. The radian does sell, but at a small KW compared to what it used 
to before the frequent float mode started popping up. If I remember 
correctly, ideally the CCs should always be in bulk charge when 
sellback occurs.


I have the CC and inverter charger float set to about 1 vdc higher then 
the inverter's sell volts, as I believe was recommended way back when. 
Hard to understand what changed, but something did. I've checked the 
relevant setpoints many times and can't find anything obviously amiss.


Does a sell mode tech note paper exist still for the Radian system? Did 
it ever? Any ideas would be greatly appreciated.


--

Kirk Herander / kirkh@vermont.solar

Owner|Principal, VT Solar, LLC

_Celebrating our 33st Anniversary 1991-2024!!_

dba Vermont Solar Engineering

802.559.1225 ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


  --

Kirk Herander / kirkh@vermont.solar

Owner|Principal, VT Solar, LLC

_Celebrating our 33st Anniversary 1991-2024!!_

dba Vermont Solar Engineering

802.559.1225 ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
--
[1] 
https://www.outbackpower.com/downloads/documents/appnotes/upgrading_1_6_63_app_note.pdf

[2] http://members.sti.net/offgridsolar/
[3] htt