Thanks, the problem is we need it to disconnect only upon loss of utility power, and it is on the battery loads panel. The panel for the HVAC is in another building that the HVAC serves.

On 8/22/2025 8:20 PM, Chris Sparadeo wrote:
Hi Chris,

I’m wondering if a load management device like this could be helpful? However, it does not discern between grid presence and island mode, so it might not fit the bill.

https://www.getstepwise.com/product?gad_source=1&gad_campaignid=22363404421&gclid=Cj0KCQjwqqDFBhDhARIsAIHTlkub687mJZYb6g0nIR33X1eA2FVY3bMc_zBxMr44IEl5a7QenVljhUgaArKeEALw_wcB <https://www.getstepwise.com/product?gad_source=1&gad_campaignid=22363404421&gclid=Cj0KCQjwqqDFBhDhARIsAIHTlkub687mJZYb6g0nIR33X1eA2FVY3bMc_zBxMr44IEl5a7QenVljhUgaArKeEALw_wcB>

Quick caveat that shedding an HVAC unit potentially mid cycle is not ideal for the health of that unit…but neither is an overload and subsequent power failure.

I do know that Lumin Smart sells remote CTs for grid detection. Might be worth a call to them to see if this fairly inexpensive product can pair with a remote contactor to open the HVAC circuit.

Best of luck!

-Chris

On Fri, Aug 22, 2025 at 3:54 PM Christopher Warfel via RE-wrenches <[email protected]> wrote:

    We installed a 4kW Outback multimode system about 8 years ago. An
    electrician came in afterwards and installed 3 heat pumps on the
    battery
    backed up power panels.  The Outback inverter disconnected on load
    every
    time there was a power outage. The electrician really messed up
    and is
    long gone. Also found out did not pull a permit. But I digress.  We
    managed to move two of the heat pump circuit breakers to the utility
    panel, so no longer on the battery backed up power panels. The third
    heat pump is the problem as it is located in an apartment building
    remote from the main house. The whole apartment subpanel,
    including the
    heat pump load  is interconnected to the "main" battery backed up
    power
    panel in the home.

    A master electrician and I are considering how to shed the apartment
    heat pump in a power outage.  We cannot easily run a separate
    circuit to
    the apartment building to pick up this load.  We have considered a
    smart
    panel, but the cost seems high for one circuit. Does anyone know of a
    power line product of RF product or similar that could operate this
    breaker when the main service panel loses power? I have been
    unsuccessful over months of sporadic research.

    Thanks in advance.


    Chris








    -- Christopher Warfel, PE ENTECH Engineering, Inc. PO Box 871, Block
    Island, RI 02807 (401) 447-5773
    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401) 447-5773
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to