That has not been my experience.  I have had to manually reboot Solark systems numerous time off grid.  If there is snow on the array or otherwise low PV output for a few days, the no load draw of the BMS then takes the battery voltage low enough to shut the battery off.   This would be a different situation with a knowledgeable owner onsite full time, but for vacation properties, it will go into complete shut down, not coming back.

Which gets into the manual and tech support for Solark:  its really not clear what the different settings do, and how they interact.  I'm sure there are engineers that know, but they aren't at Tech support. At least you can change the programming on the touch screen, and you don't have to get a quirky app up off grid to do basic changes.

BTW, what happens when the developers quit keeping the App updated, 10 years from now, and you can't access the programming? Planned Obsolescence?  That 33 yr old Trace Inverter is still doing its job.....

Ray Walters
Remote Solar



On 5/12/2025 11:33 AM, MDElectricSolar via RE-wrenches wrote:
We have been using the Solark inverter for GTBB and off grid clients. In the case of low battery cut out the solar does stay alive in the background and will recharge the batteries when the sun comes out the next day and turn itself back on and provide AC power output.

Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
707-884-1862 office
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar


On May 12, 2025, at 10:13 AM, Ray Walters via RE-wrenches <[email protected]> wrote:



So the bypass switch gets the house power on, and I too always recommend a hard bypass switch. However, you still need a 48 v power supply to get the battery system back up, and that's becoming a serious pain in my aging backside.  Until AIOs with Li+ batteries, lead acid would have enough voltage to get the charge controller to come back on, and eventually the customer could get the inverter back on too.  No special trip out.

We need an independent circuit that would sense array voltage, and wake up the battery, so it could take a charge: a backup battery for the offgrid battery.  Without that, AIOs and Li+ batteries are not self healing like Lead Acid.  We are going backwards fast, but with an amazing amount of new Chinese technology driving the jalopy in reverse.  (Danger Will Robinson)

Ray Walters
Remote Solar

On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:
We always recommend a transfer switch to bypass the inverter and send generator power to the loads. Most clients take us up on it. For retrofits, sometimes there can be space limitations, however.

As for the function of the AIO, there is no integrated mechanical bypass, and since there is an internal relay controlling the generator input (or smart load output on that breaker), I think the default function is for the relay to open when the inverter turns off. AC voltage on the load side of the breaker does not close the relay and turn the inverter back on automatically.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via RE-wrenches <[email protected]> wrote:

    All sounds wrong to me. Call Midnite.
    Typically there is a AC bypass mechanical switch that allows the
    gen to bypass the inverter and power loads.

    *Dave Angelini Offgrid Solar "we go where powerlines don't"
    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/
    <https://offgridsolar1.com/><http://members.sti.net/offgridsolar/>
    e-mail [email protected] text 209 813 0060*


    On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:

    Maybe I'm missing something, but it seems like there is a flaw
    in the logic for how generator integration works with this
    product. Unlike some of the other AIOs, you can't put the
    generator on the Grid input in an off-grid scenario. You have
    to use the Generator smart load breaker, which isn't a
    dedicated generator input, but a programmable circuit. This is
    problematic because it seemingly has a normally open internal
    relay that closes only when the inverter is ON. At least,
    that's how it seems to work in my limited experience.
    Why is this a problem? If the battery capacity drops below the
    low voltage cutoff, the inverter turns off. You have to turn
    the inverter ON for the generator relay to close so you can
    charge the battery, but since the battery is too low, the
    inverter won't turn on. You would have to reprogram the
    inverter to drop the cutoff voltage/SOC below the current
    battery state. For people who do not want to use AGS, or if AGS
    fails to start the generator for any reason, getting the
    generator to charge the battery manually is no easy task.
    Moreover, turning the generator on manually when the inverter
    is in an OFF state will not pass power to the loads, and will
    not turn the inverter ON automatically. You have to get the
    inverter turned ON somehow so that the generator power can pass
    through to the loads. And since the startup sequence for this
    inverter is very quirky, non-intuitive, and unreliable, that
    makes the problem even worse. I'm not sure if you can even turn
    the inverter ON when there is generator input and the battery
    is too low. I don't think you can because the relay is open and
    the inverter doesn't even see generator voltage when it is in
    an OFF state.
    This seems like a serious oversight and a reason to go with one
    of the other AIOs on the market. I believe the Sol-Ark 15K and
    EG4 18kPV will both immediately power loads and start charging
    when the generator is on, regardless of whether the generator
    is connected to the Grid or Generator input. Any AC input
    immediately passes through to the loads. This is because those
    inverters stay "on" when a low battery condition is met, and
    they simply stop using the battery to invert power if the
    battery conditions do not allow it, based on the settings.
    The logic of the Midnite AIOs turning "off" when battery cutoff
    is met and opening the generator relay doesn't make sense to
    me. Am I wrong about how this works?
    Jason Szumlanski
    Principal Solar Designer
    Florida Solar Design Group

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't
    work, try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't
    work, try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to