210.8 covers GFCI protection for outlets and receptacles. Hard-wired branch
circuits and feeders of a PV and ESS system are not considered outlets or
receptacles.
If I am not mistaken, each subsection specifically mentions outlets and/or
receptacles. Even the section about mini-splits is talking about cord and plug
connected units, not hard-wired appliances.
The entirety of 210 is for branch circuits only, so feeders would not fall under
this section.
Hopefully that helps!
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Thu, Mar 20, 2025 at 10:10 AM Lou Russo via RE-wrenches
<[email protected]> wrote:
> Aloha All,
>
>
> My engineer is pushing back on our design, which calls for a battery and load
> center to be installed within 6ft of the water pump and filter, the inverter
> is 7ft away. He is citing NEC 2020 210.8 and the need for GFCI protection.
>
>
> Now besides the practical reason for not doing this, I can not find a code
> reference preventing our proposed location for the battery and load center.
>
>
> This is for an off-grid new construction home with the PV equipment in the
> garage, using a Sol-Ark 15k and Discover Rack Mount batteries.
>
>
> Any input?
>
>
> Aloha,
>
>
> Lou Russo
> Owner
> [email protected] [[email protected]]
> Office - 808 345 6762
> Spree Solar Systems LLC
> CT-34322
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org [http://re-wrenches.org]
>
> List Address: [email protected]
> [[email protected]]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org]
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> [https://www.mail-archive.com/[email protected]/]
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org]
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> [http://www.re-wrenches.org/etiquette.htm]
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org [http://www.members.re-wrenches.org]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org